#94760 - 08/12/05 06:18 PM NM-B in Crawl Spaces  
BigJohn  Offline
Member
Joined: Mar 2004
Posts: 391
Boston, MA
Does the NEC allow Romex to be run across the bottoms of floor joists in crawl spaces?

This is something I see done all the time, and I thought it was legit because of the accessibility of these places, and I see it pass on inspected new construction. But I can't find any article allowing it or exempting crawlspaces from 300.4.

Maybe everyone (rightfully) assumes that no inspector in their right mind is going into that crawl space to enforce this...?

-John

[This message has been edited by BigJohn (edited 08-12-2005).]


2017 / 2014 NEC & Related Books and Study Guides

#94761 - 08/12/05 07:02 PM Re: NM-B in Crawl Spaces  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
I suspect they will cite;
334.15 Exposed Work.
In exposed work, except as provided in 300.11(A), the cable shall be installed as specified in 334.15(A) through (C).
(A) To Follow Surface. The cable shall closely follow the surface of the building finish or of running boards.

... if anyone is willing to crawl in there for a peek. [Linked Image]


Greg Fretwell

#94762 - 08/13/05 08:33 AM Re: NM-B in Crawl Spaces  
macmikeman  Offline
Member
Joined: Jul 2002
Posts: 717
Honolulu, Hawaii
It's not allowed where I'm at, unless # 6 guage or larger cable. I allways run along the face of the joists and drill thru cross blocking. Usually there is a beam holding up them joist and I staple to the face of that for perpendicular to the joist runs.



Member Spotlight
Posts: 362
Joined: April 2003
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7526 MB (Peak: 0.8744 MB) Zlib enabled. Server Time: 2017-10-19 23:41:56 UTC