If I have 3 air conditioning condensers on a feeder and the info on the name plates say Minimum circuit 36a. - What minimum size feeder conductor should I install and how should it be fused?
Each condensing unit has 2 motors and a crankcase heater.
George Little
|
|
|
|
Joined: Jul 2004
Posts: 10,011 Likes: 37
Member
|
Interesting question ... again. ;-) Does voltage drop figure in here? Are you going for the minimum that is legal (2 ga with 125 O/C) or what would give better reliability (1 ga and 150) both using 240.4(B). I would want to use staggered timeouts on the compressor time delays so you wouldn't have 3 liquid slugged compressors in locked rotor at the same time on a power hit.
Greg Fretwell
|
|
|
|
Joined: Jan 2004
Posts: 1,507
OP
Member
|
Greg- I would say that #2 and 125a OC Minimum.
Some would say #1 and it probably would be a better design choice for the reasons you stated. Some inspectors maintain that you add an extra 25% of the largest motor. Some inspectors will take the largest motor of an individual A/C unit and add up all the other motors and come up with a smaller conductor yet.
George Little
|
|
|
|
Joined: Jul 2004
Posts: 10,011 Likes: 37
Member
|
I think we already covered that ground last time. Some might even argue that the 125% thing has been done 3 times in that engineered number on the HVAC label. If the run is not excessive the #2 should be OK. The only caveat I would have is staggering the time out relays and that is really a design issue.
Greg Fretwell
|
|
|
|
Joined: Jan 2005
Posts: 5,476 Likes: 3
Cat Servant Member
|
Every A/C I've seen also state, on the nameplate, "minimum circuit ampacity."
Since this is one of the "exceptions" to generalbranch circuit sizing rules, an example would be a specification of "25 amp" minimum ampacity being provided by #12 conductors.
Now, if you were to use a single feeder, and tap off it to all three condensers, I would forget the "minimum circuit ampacity" and size the feeder according to "full load amps" and motor feed rules.
|
|
|