Pool motor #94649 08/04/05 08:19 AM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline OP
Member
Does the pool filter motor have to be on a dedicated feed?
Can you install the convience receptacle on the same feed as the pool motor?
Any thoughts?

2017 / 2014 NEC & Related Books and Study Guides
Re: Pool motor #94650 08/04/05 09:59 AM
Joined: May 2005
Posts: 706
T
Tiger Offline
Member
I don't find any requirement for the pool pump to be on a dedicated circuit without other outlets.

Dave

Re: Pool motor #94651 08/04/05 02:41 PM
Joined: Apr 2004
Posts: 60
M
markp Offline
Member
If the pool pump is hardwired, then this rule applies:

210.23(A)(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures), shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.

So if you want receptacles on a hard wired motor circuit, then it can only draw half of the circuit's rating (which isn't likely with most 120V pool pumps).


Mark
Kent, WA
Re: Pool motor #94652 08/04/05 03:15 PM
Joined: Jul 2004
Posts: 9,513
G
gfretwell Offline
Member
The light circuit would be a better candidate for the receptacle but be aware of the "unspliced EGC" rule when you lay it out.
I pulled 2 EGCs when I did mine. The unspliced one went to the J box and another was used for the receptacle, switch etc.
My pump is 240v. I figure the I2R savings will pay for the extra few bucks I paid for the breaker ... eventually.


Greg Fretwell
Re: Pool motor #94653 08/04/05 03:37 PM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline
Member
680.22 (A) (3) "Dwelling unit(s). Where a permanently installed pool is installed at a dwelling unit(s), no fewer than one 125 volt 15 or 20 ampere receptacle on a general purpose branch circuit shall be located not less than 3.0m (10ft) from, and not more than 6.0 m (20ft) from, the inside wall of the pool."

I would say a circuit for the pool motor is not a general purpose branch circuit, thus the convienience receptacle can not be fed from that circuit.

Re: Pool motor #94654 08/04/05 04:58 PM
Joined: Jul 2004
Posts: 9,513
G
gfretwell Offline
Member
Branch Circuit, General-Purpose. A branch circuit that supplies two or more receptacles or outlets for lighting and appliances.

I suppose it all depends on if a pool pump is an "appliance" and if the light is "lighting".
They didn't have any problem with my receptacle on the same circuit as the wet niche light. (Lee Co Fla)


Greg Fretwell
Re: Pool motor #94655 08/04/05 05:25 PM
Joined: Dec 2004
Posts: 1,064
D
Dnkldorf Offline
Member
gfretwell, I don't understand the post about 2 equipment grounds and how that plays into line loss. I2R

Can you explain?


Dnk.....

Re: Pool motor #94656 08/04/05 05:58 PM
Joined: Jul 2004
Posts: 9,513
G
gfretwell Offline
Member
With a 240v motor the loss in the wire will be less (increases with the square of current)
A wet niche light required an unspliced ground to the J box (with a few exceptions).
Since I was also feeding another circuit from this (the receptacles) it was easier to just pull 2 EGCs and avoid any confusion.


Greg Fretwell
Re: Pool motor #94657 08/04/05 06:11 PM
Joined: Dec 2004
Posts: 1,064
D
Dnkldorf Offline
Member
Sorry, I didn't notice you switched topics in your post.

Somehow(I dunno),I thought you were suggesting an EGC had something to do with line loss.


Dnk......

Re: Pool motor #94658 08/04/05 10:48 PM
Joined: Jul 2004
Posts: 9,513
G
gfretwell Offline
Member
I will plead temporary insanity. I was digging in the yard and I was delerious when I came back in to post that. ;-)

Sorry for the confusion.


Greg Fretwell
Page 1 of 3 1 2 3

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
pcsailor
pcsailor
Minneapolis, MN, USA
Posts: 21
Joined: September 2019
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
268,614 Are you busy
202,965 Re: Forum
191,341 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3