#94649 - 08/04/05 08:19 AM Pool motor  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Does the pool filter motor have to be on a dedicated feed?
Can you install the convience receptacle on the same feed as the pool motor?
Any thoughts?


2017 / 2014 NEC & Related Books and Study Guides

#94650 - 08/04/05 09:59 AM Re: Pool motor  
Tiger  Offline
Member
Joined: May 2005
Posts: 706
Crystal Lake, IL USA
I don't find any requirement for the pool pump to be on a dedicated circuit without other outlets.

Dave


#94651 - 08/04/05 02:41 PM Re: Pool motor  
markp  Offline
Member
Joined: Apr 2004
Posts: 60
Kent, WA, USA
If the pool pump is hardwired, then this rule applies:

210.23(A)(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures), shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.

So if you want receptacles on a hard wired motor circuit, then it can only draw half of the circuit's rating (which isn't likely with most 120V pool pumps).


Mark
Kent, WA

#94652 - 08/04/05 03:15 PM Re: Pool motor  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,124
Estero,Fl,usa
The light circuit would be a better candidate for the receptacle but be aware of the "unspliced EGC" rule when you lay it out.
I pulled 2 EGCs when I did mine. The unspliced one went to the J box and another was used for the receptacle, switch etc.
My pump is 240v. I figure the I2R savings will pay for the extra few bucks I paid for the breaker ... eventually.


Greg Fretwell

#94653 - 08/04/05 03:37 PM Re: Pool motor  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
680.22 (A) (3) "Dwelling unit(s). Where a permanently installed pool is installed at a dwelling unit(s), no fewer than one 125 volt 15 or 20 ampere receptacle on a general purpose branch circuit shall be located not less than 3.0m (10ft) from, and not more than 6.0 m (20ft) from, the inside wall of the pool."

I would say a circuit for the pool motor is not a general purpose branch circuit, thus the convienience receptacle can not be fed from that circuit.


#94654 - 08/04/05 04:58 PM Re: Pool motor  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,124
Estero,Fl,usa
Branch Circuit, General-Purpose. A branch circuit that supplies two or more receptacles or outlets for lighting and appliances.

I suppose it all depends on if a pool pump is an "appliance" and if the light is "lighting".
They didn't have any problem with my receptacle on the same circuit as the wet niche light. (Lee Co Fla)


Greg Fretwell

#94655 - 08/04/05 05:25 PM Re: Pool motor  
Dnkldorf  Offline
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
gfretwell, I don't understand the post about 2 equipment grounds and how that plays into line loss. I2R

Can you explain?


Dnk.....


#94656 - 08/04/05 05:58 PM Re: Pool motor  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,124
Estero,Fl,usa
With a 240v motor the loss in the wire will be less (increases with the square of current)
A wet niche light required an unspliced ground to the J box (with a few exceptions).
Since I was also feeding another circuit from this (the receptacles) it was easier to just pull 2 EGCs and avoid any confusion.


Greg Fretwell

#94657 - 08/04/05 06:11 PM Re: Pool motor  
Dnkldorf  Offline
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
Sorry, I didn't notice you switched topics in your post.

Somehow(I dunno),I thought you were suggesting an EGC had something to do with line loss.


Dnk......


#94658 - 08/04/05 10:48 PM Re: Pool motor  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,124
Estero,Fl,usa
I will plead temporary insanity. I was digging in the yard and I was delerious when I came back in to post that. ;-)

Sorry for the confusion.


Greg Fretwell

Page 1 of 3 1 2 3

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 15 (0.004s) Memory: 0.8195 MB (Peak: 0.9949 MB) Zlib enabled. Server Time: 2017-10-23 05:57:33 UTC