Pool motor #94649
08/04/05 08:19 AM
08/04/05 08:19 AM
H
harold endean  Offline OP
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Does the pool filter motor have to be on a dedicated feed?
Can you install the convience receptacle on the same feed as the pool motor?
Any thoughts?

2017 / 2014 NEC & Related Books and Study Guides
Re: Pool motor #94650
08/04/05 09:59 AM
08/04/05 09:59 AM
T
Tiger  Offline
Member
Joined: May 2005
Posts: 706
Crystal Lake, IL USA
I don't find any requirement for the pool pump to be on a dedicated circuit without other outlets.

Dave

Re: Pool motor #94651
08/04/05 02:41 PM
08/04/05 02:41 PM
M
markp  Offline
Member
Joined: Apr 2004
Posts: 60
Kent, WA, USA
If the pool pump is hardwired, then this rule applies:

210.23(A)(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures), shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.

So if you want receptacles on a hard wired motor circuit, then it can only draw half of the circuit's rating (which isn't likely with most 120V pool pumps).


Mark
Kent, WA
Re: Pool motor #94652
08/04/05 03:15 PM
08/04/05 03:15 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,198
Estero,Fl,usa
The light circuit would be a better candidate for the receptacle but be aware of the "unspliced EGC" rule when you lay it out.
I pulled 2 EGCs when I did mine. The unspliced one went to the J box and another was used for the receptacle, switch etc.
My pump is 240v. I figure the I2R savings will pay for the extra few bucks I paid for the breaker ... eventually.


Greg Fretwell
Re: Pool motor #94653
08/04/05 03:37 PM
08/04/05 03:37 PM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
680.22 (A) (3) "Dwelling unit(s). Where a permanently installed pool is installed at a dwelling unit(s), no fewer than one 125 volt 15 or 20 ampere receptacle on a general purpose branch circuit shall be located not less than 3.0m (10ft) from, and not more than 6.0 m (20ft) from, the inside wall of the pool."

I would say a circuit for the pool motor is not a general purpose branch circuit, thus the convienience receptacle can not be fed from that circuit.

Re: Pool motor #94654
08/04/05 04:58 PM
08/04/05 04:58 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,198
Estero,Fl,usa
Branch Circuit, General-Purpose. A branch circuit that supplies two or more receptacles or outlets for lighting and appliances.

I suppose it all depends on if a pool pump is an "appliance" and if the light is "lighting".
They didn't have any problem with my receptacle on the same circuit as the wet niche light. (Lee Co Fla)


Greg Fretwell
Re: Pool motor #94655
08/04/05 05:25 PM
08/04/05 05:25 PM
D
Dnkldorf  Offline
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
gfretwell, I don't understand the post about 2 equipment grounds and how that plays into line loss. I2R

Can you explain?


Dnk.....

Re: Pool motor #94656
08/04/05 05:58 PM
08/04/05 05:58 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,198
Estero,Fl,usa
With a 240v motor the loss in the wire will be less (increases with the square of current)
A wet niche light required an unspliced ground to the J box (with a few exceptions).
Since I was also feeding another circuit from this (the receptacles) it was easier to just pull 2 EGCs and avoid any confusion.


Greg Fretwell
Re: Pool motor #94657
08/04/05 06:11 PM
08/04/05 06:11 PM
D
Dnkldorf  Offline
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
Sorry, I didn't notice you switched topics in your post.

Somehow(I dunno),I thought you were suggesting an EGC had something to do with line loss.


Dnk......

Re: Pool motor #94658
08/04/05 10:48 PM
08/04/05 10:48 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,198
Estero,Fl,usa
I will plead temporary insanity. I was digging in the yard and I was delerious when I came back in to post that. ;-)

Sorry for the confusion.


Greg Fretwell
Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 68
Joined: January 2002
Show All Member Profiles 