Huh? #94610
08/03/05 06:21 PM
08/03/05 06:21 PM
D
Dnkldorf  Offline OP
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
Single story commercial building.
Undergoing some renovation. Not by us, but by the construction company EC.

Anyway:

Exsisting romex from who knows how long ago, at least 15 yrs?

So why does the electrical inspector come in one day and say, "all this romex has to go".

He wants it all tore out and replaced with mc.

How does this happen?


Dnk......

2017 / 2014 NEC & Related Books and Study Guides
Re: Huh? #94611
08/03/05 07:27 PM
08/03/05 07:27 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
They may have local ammendment to code restricting use of NM in commercial. My area does... MC and pipe only!

If it were to existing code at the time of install, he should not be asking for it to be removed.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Huh? #94612
08/03/05 07:33 PM
08/03/05 07:33 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,024
Brick, NJ USA
DNK:
What is the occupancy of the new tenant??
Medical??
Is the new 'use' using a plenum ceiling?

If it was 'to code' when installed, then it should be able to stay.

John


John
Re: Huh? #94613
08/03/05 08:04 PM
08/03/05 08:04 PM
C
Celtic  Offline
Member
Joined: Feb 2005
Posts: 361
NJ
Another question need to be answered:


What percentage of the property is under going the renovation?
Some jurisdictions require full compliance with active code after 50% renovation.


~~ CELTIC ~~
...-= NJ =-...
Re: Huh? #94614
08/03/05 08:18 PM
08/03/05 08:18 PM
D
Dnkldorf  Offline OP
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
To answer some of your replies:

1. maybe 10% of the building being retrofitted.
2. No medical use at all, renovating being done to make old cubicle area into offices for new engineering staff. New walls, dividers and such.
3. Same ole tennant, been in the building for as long as I can remmember.
4. All new ac unit trunks being pu in, same ac units though, no plenum cieling that I know about.


I have no clue how he can justify this, like I said this was an electrical inspector, not a building inspector or fire marshall.

Dnk.....

Re: Huh? #94615
08/04/05 03:43 PM
08/04/05 03:43 PM
D
Dnkldorf  Offline OP
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
And the answer is:

Exsisting romex above a drop must come out. All of it.

Romex in walls can stay, then go to j-box and then mc above the drop cieling.

Anyone have a code reference for this?


Dnk.......

Re: Huh? #94616
08/05/05 02:33 PM
08/05/05 02:33 PM
D
Dnkldorf  Offline OP
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
FYI

Talked to inspector, because only 10% is being renovated now, permit that was pulled calls for over 50% of the building to be renovated. Work is being done in phases, rather than all at once, therefore romex must come out.

Dnk........

Re: Huh? #94617
08/06/05 04:19 AM
08/06/05 04:19 AM
W
William Runkle  Offline
Member
Joined: Feb 2003
Posts: 27
Dowagiac, Michigan U.S.A.
Question where is this one story commerical building? Is it in a fire zone? It could be a local code requirement. And possibly the original wiring in non-metallic sheath cable was not inspected or had a permit so the EC now has to straighten this problem out.


William Runkle
Re: Huh? #94618
08/06/05 06:34 AM
08/06/05 06:34 AM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Code reference is NEC 2002 334.12(A)(1)


Ron

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
BigB 4
Popular Topics(Views)
249,474 Are you busy
187,390 Re: Forum
176,732 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.034s Queries: 14 (0.009s) Memory: 1.0013 MB (Peak: 1.1709 MB) Zlib enabled. Server Time: 2018-09-26 08:44:29 UTC