Are you talking about a fire watch tower type thing? (I have always day dreamed about having one...)
Or, like a large open Kazzebo type thing? Some pillars and a roof, no walls. I think thats what you're getting at? Figure it all NEMA 3 at the very least, for exposure to weather, and wet/damp location.
Then as for GFI's considering it is residential, all
Calling it an out building, or garage...
210(a)2 Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use.
(3) Outdoors
Same for commercial if it were:
511.12 Ground-Fault Circuit-Interrupter Protection for Personnel.
All 125-volt, single-phase, 15- and 20-ampere receptacles installed in areas where electrical diagnostic equipment, electrical hand tools, or portable lighting equipment are to be used shall have ground-fault circuit-interrupter protection for personnel.
Even if it doesn't fit a catagory, some common sense is in order in design, outside of the code. GFI all the 15 and 20A recepticals. Taking a knee on a concrete slab is like sticking your leg in tub while holding say a drill.... (CB's would be cheaper for this type of thing.) NEMA3 all around the wet areas at the very least, and cord covers if applicable in 406.8.