#94448 07/30/05 06:34 AM
Joined: Jul 2005
Posts: 73
S
Member
I am an electrician for a small 250 bed hospital.I should say I am thee electrician for the hospital.Anyway we built a new facility 3 years ago.each O.R. suite has its own 120/208V 3 phase panelboard.There is no ground isolation, line isloation monitors or gfcis in the rooms.The rooms are anything but a dry location.The way I understand the code you must have gfcis and if you can't tolerate nuisance tripping you must have a ground isloation panel.Any clarity will help.

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#94449 07/31/05 07:21 AM
Joined: May 2002
Posts: 1,716
R
Member
Don, you are absolutly correct. In N.C. all O.R.'s must be supplied with Isolated Power systems so no problem here. I thought FL still mandated them as well. (guess I was wrong)

For an article from another frustrated Facilty Person on the Wet Location topic, click the link below.
http://www.healthcareengineering.net/archive/phile/Article.aspx?aid=192

And a little more information.
http://www.healthcareengineering.net/archive/phile/Article.aspx?aid=190


Roger



[This message has been edited by Roger (edited 07-31-2005).]

#94450 07/31/05 08:45 AM
Joined: Jul 2005
Posts: 73
S
Member
The way I see it it is an accident waiting to happen.I have found extension cords in buckets of water the staff was used to isolated power systems in our other facility.However they seem pretty clueless to the dangers.The only way I see how they got around A.H.C.A was they must have insisited they were only going to dry procedures.Then I still feel they at least need gfcis.The really odd thing is they are still grouding patients is this crazy or is it just me.If I mention my concerns to the chiefs they just think well it passed inspection so it must be right.I would like to install the right equipment but I feel it is a slippery slope does profit come before safety.I have been trying to correct this issue for some time.I don't really want to call it to inspectors attention if I can help it but if I am sure I am right on this and they don't cough up the cash to fix it.I almost feel obligated to do something about it.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,157
Joined: May 2003
Top Posters(30 Days)
NORCAL 3
Popular Topics(Views)
287,941 Are you busy
220,081 Re: Forum
206,077 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5