Friday we had the main service (277/480V) shut down on a job I am finishing up. I took that opportunity to pull the neutral disconnect link and check for neutral to ground connections. Sure enough, there were some. We traced them down to a couple of pinched neutral ballast wires in the ReLock lighting system. The last one we found was (is) in the exterior metal halide wall packs. Since these fixtures were not in our scope of work (installed by core and shell contractor, powered by us) we left it alone and today I wrote a letter to the owner via the General Contractor notifying them of the problem.
I am a little worried that I may have opened up a can of worms. I am now being told by my PM that he had a lot of trouble in getting clear readings with HID fixtures in the past. (This was in the infamous Huntington Beach area for those of you from around here) They have a connection or leakage that gives you the impression there is a bad connection.
Is this common with HID fixtures? I have always thought the neutral to ground reading should be clear no matter what. Does the circuitry in these fixtures not allow this? [Linked Image]
Posted on: Mike Holt & Electrical-Contractor.net

Work Gear for Electricians and the Trades
Re: Neutral To Ground #9423
04/30/02 07:11 PM
04/30/02 07:11 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,274
Fullerton, CA USA
Nick,
I replaced the cap in a M/H HID, and it seemed to "correct" the equivalent problem.
Also, one doesn't need to use a "supermeter" to satisfy the folks in HB.
Of course, I'd never suggest that you cheat, but some of the people that pass this test do it with a battery and a light bulb!

[This message has been edited by electure (edited 04-30-2002).]

Re: Neutral To Ground #9424
04/30/02 09:51 PM
04/30/02 09:51 PM
N
Nick  Offline OP
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
Thanks Scott,
The job I am doing is in Ontario and already finaled. We didn't have the test to go through. The job I was referring to in Huntington was some fancy hotel my PM did when he was a GF. I was just being proactive trying not to leave this job with known problems. Turns out it has come around to bit me. The Architect and engineer have responded it is in my specs to fix the problem. [Linked Image] Even though we did not supply or install the lights or branch circuiting to them. I haven't double checked yet to see if I have an out but as well written as there specs were they are probably right. What's that saying again?... Nice guys Finnish where?

[Note to self...Don't be so conscientious in the future.]

[This message has been edited by Nick (edited 04-30-2002).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 68
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
BigB 4
Popular Topics(Views)
249,456 Are you busy
187,375 Re: Forum
176,715 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.004s) Memory: 0.9518 MB (Peak: 1.0743 MB) Zlib enabled. Server Time: 2018-09-25 17:03:56 UTC