Is this legal or not? I know you can install one above a suspended ceiling but can you if it is a plenum ceiling?

Horizontal Ad
Joined: Jan 2004
Posts: 1,507
G
Member
I don't see a problem installing a transformer in a space above the ceiling as discribed in 300.22(C). If however, it is indeed a plenum as discribed in (B) you may have a problem. There are other considerations in Article 450 that need to be addressed also such as accessibility and size of transformer.


George Little
Joined: Feb 2005
Posts: 44
B
Member
It is a 45 KVA transformer and it is vented.
I have never done this before as I was told it would have to be a sealed transformer or in an enclosure. It was explained that the dust and lint that is being sucked into the plenum could build up on the windings of a vented transformer and the heat from the transformer could ignite it. This installation would take place in a clothing store in a mall.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Radar
Radar
Los Angeles
Posts: 349
Joined: April 2004
Top Posters(30 Days)
Popular Topics(Views)
338,130 Are you busy
263,580 Re: Forum
243,616 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5