#94051 07/04/05 08:44 PM
Joined: Apr 2002
Posts: 257
M
Member
I am pretty sure that it is not allowed but I can't find where it says that type SE or SER cable cannot be installed in conduit for a complete run of say...60 feet.

I have to inspect a job that my electrician wannabe brother-in-law did where I know that he installed two 200a subfeeds in a small garage in PVC conduit using SER cable (4/0).

Anyone I know would have used THHN and it would not be an issue but he doesn't know any better.

Help me justify failing the installation or tell me if I'm wrong.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#94052 07/04/05 09:06 PM
Joined: Jan 2005
Posts: 5,422
Likes: 1
Cat Servant
Member
I have reviewed both the NEC and the UL "White Book." Neither specifically address the issue- it appears that no one considered it.
Type USE is severely limited in its' indoor applications, but there is no such limit on SE.

Since it is not specifically prohibited, I would say it is allowed- especially if there is a desire for additional mechanical protection.
However, I would consider the issue of de-rating, as is done with Romex. While there is no official temperature rating for the assembly (unlike Romex, which is 60 degrees), it seem reasonable to treat SE in a like manner.

#94053 07/04/05 10:06 PM
Joined: Jul 2004
Posts: 9,883
Likes: 27
G
Member
The most immediate issue would be wire fill. It is considered one conductor with the diameter of the maximum dimension so a pipe fills up fast.


Greg Fretwell
#94054 07/04/05 10:23 PM
Joined: Jan 2004
Posts: 1,507
G
Member
I looked in the '02 NEC at Article 352 Sect 352.22 and it seens to say no- SER installed in RNMC would not be a code compliant installation because SER is not specifically identified for use in a raceway. Some cables are identified as being acceptable when installed in a raceway: Fire alarm cable (760.54) NM cable for short sections (334.15 (B)) Class 2 & 3 cables (725.55(C)). I do not see that kind of wording for SER or SE cables.

Now if you go to the '05 code Article 352 Section 352.22 is worded diffeently and it might change things. Now why anyone would want to install a raceway system and then pull in SER or SE cable is beyond me. The chance of overfilling the raceway or damaging the cable is very high.


George Little
#94055 07/04/05 10:33 PM
Joined: Jan 2004
Posts: 1,507
G
Member
I almost forgot- If this is an underground installation then the Listing for SE or SER cable would be violated since it is only listed for above ground.


George Little
#94056 07/05/05 07:11 AM
Joined: Jan 2005
Posts: 3
E
Junior Member
I came across the same situation: SER in 21/2" pvc #80 outside od house. 50' run,2-90% and 1-LB then to meter main. Cable tech. drill a hole in the conduit and shorted out the feed. I told them that I needed to replace the conduit and install the correct cable (THHN). What you had was a violation. They said prove it. I opened up the code book and look & look, but could not find any thing to support my statement. It would seem that SER in such a run of pvc would be wrong. Maybe ampacity,number of conductors in conduit would play out in the code? Would that large of SER 200amp size bent in a LB a violation. That must have been someting to install. Or my last one was "not completing conduit run before installing cable". ????

#94057 07/05/05 10:37 AM
Joined: Apr 2004
Posts: 60
M
Member
George, what about 338.10(B)(4)? This says for interior runs of SE, you use the part I and II rules for NM cable. But the NM rules only seem to get you a physical protection run of conduit and not necessarily a complete conduit system.


Mark
Kent, WA
#94058 07/05/05 08:24 PM
Joined: Jun 2004
Posts: 613
S
Member
312.5(C) requires cables to be secured to each cabinet,cutout box or meter socket enclosure...

314.17(B) requires the cable to be secured to boxes and conduit bodies...

These rules would seem to disallow the use of type SE cable in a raceway...

shortcircuit

#94059 07/05/05 09:01 PM
Joined: Apr 2002
Posts: 257
M
Member
Went to inspect it today. two runs about 100' each. He said that he stripped the insulation off of the entire cable before installation.

He's driving me nuts. What would you do?

#94060 07/05/05 10:48 PM
Joined: Jul 2004
Posts: 9,883
Likes: 27
G
Member
He sure wouldn't like my answer.
When you strip the jacket off any cable assembly you end up with an unlisted/unlabelled conductor of unknown properties.


Greg Fretwell
Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Top Posters(30 Days)
NORCAL 1
Popular Topics(Views)
313,348 Are you busy
239,240 Re: Forum
222,992 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5