ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photo of the Week:

1898 Underground Hydro Plant
1898 Hydro Plant

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
1 members (Scott35), 56 guests, and 29 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Jul 2004
Posts: 10,001
Likes: 35
G
Member
In reference to the electrical elements of a pool, is a screen cage a permanent barrier.
examples;
Can a receptacle outside the cage, 11 feet from the pool, be counted as the required one?
If it is only 4 feet from the pool but outside the screen is it OK?


Greg Fretwell
Horizontal Ad
Joined: Jan 2004
Posts: 1,507
G
Member
Well Greg, I would make the call that the receptacle located 4 feet from the pool has to go and the receptacle located 11 feet from the pool meets the requirement of 680.22(A)(3). I am making that call based on 680.22(A)(6) and based on the fact that one can "pierce" the screen cage [Linked Image]

Some times we have to put on the hat of King Solomon.


George Little
Joined: Jun 2005
Posts: 12
D
Member
I would think the screen would be a permanent barrier. We are know required to supply, at back of house, a receptacle inside and outside of cage. AHJ says the required back outlet inside of screen is not accessable to the rest of outside. If they require an outlet inside and outside of screen enclosure because of accessability, then the screen would be considered a barrier. Plus it's not considered the required within 20 foot rule if outside the screen enclosure.
I laugh at the requirement of a receptacle within 20 foot of pool, but greater than 10 foot, unless physically impossible to keep 10 foot (680.22 A.4)than 5 foot or greater is OK. Why require an outlet and potential hazard with (680.22 A.3). Swim at your own risk!


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,438
Joined: February 2004
Top Posters(30 Days)
Popular Topics(Views)
333,172 Are you busy
258,339 Re: Forum
239,913 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5