Joined: Oct 2000
Posts: 2,749
Member
Quote
Joe:

Is there anywhere in the NEC or the NESC that requires bollards by a utility transformer, or any transformer installation be bonded???

Paul O'Connell

I would check with the local utility company since they may not be covered by the NEC. As far as the NESC, I don't know. I am sure someone will come forward and reply.


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Apr 2002
Posts: 7,380
Likes: 7
Member
Joe:
Our utility (PSE&G) has the bollard requirements spelled out within there specification book. It basically applies to pad mounts that may be subject to physical damage from vehicles.

They also spec bollards to protect CT cabinets, meter equipment etc., that is within their jurisdiction.

These must be NESC rules/requirements.

As to bonding, the utility pad mounts are bonded when they arrive on site; we provide grd rod(s) based on their specs on the primary side.

John


John
Joined: Jan 2005
Posts: 5,441
Likes: 2
Cat Servant
Member
I repeat Hotline's post: this is a PoCo issue, they are the AHJ...check their standards.

The NEC does require protection from traffic- and that's it. PoCo standards typically tell you how many, how tall, sunk how deep, made how, painted what color, etc. They will also specify WHERE to place the bollards- can't have a bollard blocking line tool access, can we?

Joined: Jul 2005
Posts: 56
P
Member
I have looked in the NEC, IEEE handbook, NESC handbook,in 40 years I have never seen it done, bollard bonding along with bonding the manhole cover, yet I am being told by a sub contractor for the DOE hired to do NEC inspections that these are both code violations. I would appreciate any input available.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 99
Joined: August 2003
Top Posters(30 Days)
maxecn 5
Admin 3
Popular Topics(Views)
317,837 Are you busy
242,668 Re: Forum
226,704 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5