Bollards by a utility transformer #94021 06/30/05 05:56 PM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
Quote
Joe:

Is there anywhere in the NEC or the NESC that requires bollards by a utility transformer, or any transformer installation be bonded???

Paul O'Connell

I would check with the local utility company since they may not be covered by the NEC. As far as the NESC, I don't know. I am sure someone will come forward and reply.


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Bollards by a utility transformer #94022 06/30/05 06:24 PM
Joined: Apr 2002
Posts: 7,191
HotLine1 Offline
Member
Joe:
Our utility (PSE&G) has the bollard requirements spelled out within there specification book. It basically applies to pad mounts that may be subject to physical damage from vehicles.

They also spec bollards to protect CT cabinets, meter equipment etc., that is within their jurisdiction.

These must be NESC rules/requirements.

As to bonding, the utility pad mounts are bonded when they arrive on site; we provide grd rod(s) based on their specs on the primary side.

John


John
Re: Bollards by a utility transformer #94023 06/30/05 08:00 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
I repeat Hotline's post: this is a PoCo issue, they are the AHJ...check their standards.

The NEC does require protection from traffic- and that's it. PoCo standards typically tell you how many, how tall, sunk how deep, made how, painted what color, etc. They will also specify WHERE to place the bollards- can't have a bollard blocking line tool access, can we?

Re: Bollards by a utility transformer #94024 07/03/05 11:52 AM
Joined: Jul 2005
Posts: 56
P
Paul O'Connell Offline
Member
I have looked in the NEC, IEEE handbook, NESC handbook,in 40 years I have never seen it done, bollard bonding along with bonding the manhole cover, yet I am being told by a sub contractor for the DOE hired to do NEC inspections that these are both code violations. I would appreciate any input available.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
268,524 Are you busy
202,925 Re: Forum
191,318 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3