Are concentric or eccentric knockouts evaluated for bonding? #93789 06/18/05 01:06 AM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
Just to be sure, you should read the following information very carefully, when evaluating concentric and eccentric knockouts:
http://www.ul.com/regulators/knockouts.cfm


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Are concentric or eccentric knockouts evaluated for bonding? #93790 06/18/05 04:16 AM
Joined: Feb 2003
Posts: 27
W
William Runkle Offline
Member
Intresting have you seen any boxes or cabinets marked? I will be looking for them but I still probably still bond bush so not to upset an inspector who hasn't seen the marking, plus just assurance that it is bonded and be ease of mind.


William Runkle
Re: Are concentric or eccentric knockouts evaluated for bonding? #93791 06/18/05 06:14 PM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
Yes,

The following table summarizes the box and enclosure categories where such an evaluation is available and how to identify compliant products that can be installed according to the exception to Section 250.97.

Category Code
Product Category
Concentric and eccentric knockouts evaluated for bonding?

BGUZ
Boxes, Junction and Pull
Only when product is marked*

CYIV
Cabinets and Cutout Boxes
Only when product is marked*

QCIT
Metallic Outlet Boxes
All products comply


* Products Listed for these applications are provided with a marking, such as "Concentric (or eccentric) knockouts suitable for bonding conduits for non-service conductors."


Joe Tedesco, NEC Consultant
Re: Are concentric or eccentric knockouts evaluated for bonding? #93792 06/23/05 04:38 PM
Joined: Jun 2003
Posts: 1,143
D
DougW Offline
Member
+1 for the additional bonding.

The $8 in parts is worth more than 20 minutes proving your point to an inspector.

Re: Are concentric or eccentric knockouts evaluated for bonding? #93793 06/23/05 05:40 PM
Joined: Dec 2004
Posts: 94
T
tkb Offline
Member
Just knock out the KO all the way and use reducing washers. They are UL listed for grounding. Save the cost of the bond bushings.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
268,551 Are you busy
202,946 Re: Forum
191,328 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3