#93774 06/14/05 09:07 PM
Joined: Aug 2001
Posts: 466
Likes: 1
J
Jim M Offline OP
Member
I just got a red tag for not having a main in a subpanel in a residential detached garage. Panel is a C-H 4/8 MLO with 2 circuits installed. AHJ is using 225-31 as the reason.

Is anyone elses area requiring this. I guess I was thinking 6 or less breakers did not need a main.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jan 2003
Posts: 4,391
I
Moderator
In my opinion you are correct.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
225.33(A) General. The disconnecting means for each supply permitted by 225.30 shall consist of not more than six switches or six circuit breakers mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard. There shall be no more than six disconnects per supply grouped in any one location.


Greg Fretwell
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
For a separate building, such as a detached garage, you are required to have a disconnecting means on the building. In this area, I typically have a 'safety switch' mounted on the outside, feeding the panel directly behind it (on the inside). A 'main breaker' in the panel is another way to do it- but is usually more expensive- and our AHJ likes the disconnect on the outside anyway.

There is one exception- no such disconnect is necessary if you're running only one circuit- and "circuit" is vague enough to include a single multi-wire branch circuit (or what we normally think of as two circuits). Assuming that you are using both full-size breaker spaces for a pair of full size breakers, you might be able to argue that you have but a single multi-wire circuit, with the breakers simpling being an additional, not required, disconnecting means.

Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
IMO (and that of the Handbook) 225 section II effectively says to treat each separate building like it has it's own service entrance. Except when only one circuit (specifically allows multi-wire) is in the separate building.

225.30 only one source can feed the separate building (230.2, 230.40)
225.31 all ungrounded conductors must be disconnected (230.70)
225.32 disconnect where power enters building (230.71(A))
225.33 number of mains (230.71)
225.34 group the mains (230.72)
225.35 accessible to occupants (230.70(A)(1), 230.72(C))
225.36 suitable for service entrance(230.70(C))

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
Don't ignore 225.36 exception
Exception: For garages and outbuildings on residential property, a snap switch or a set of 3-way or 4-way snap switches shall be permitted as the disconnecting means.


Greg Fretwell
Joined: Jan 2005
Posts: 316
L
Member
Where I live if the sub panel is in a ATTACHED garage no main needed - in a DETACHED garage a main is required by ahj

Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
Thank you, JBD, for taking the time to break down all the code citations I was alluding to!