Question for load calculation.
Ive got 2- 50 amp 480 volt 1 ph 70% duty welders.
Using the multiplier .84 for the 70 % duty cycle, I am to use this on the first 2 welders correct?
Also,if using a 3rd welder,using the 85 %,is this 85% of the .84 multiplier.
Your opinions appreciated

2017 / 2014 NEC & Related Books and Study Guides
Re: art 630 #93752
06/09/05 01:45 AM
06/09/05 01:45 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,373
Estero,Fl,usa
That's the way 630.11(B) reads to me

(B) Group of Welders. Conductor ampacity shall be based on the individual currents determined in 630.11(A) as the sum of 100 percent of the two largest welders, plus 85 percent of the third largest welder...


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
257,162 Are you busy
192,980 Re: Forum
182,639 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 14 (0.004s) Memory: 0.9424 MB (Peak: 1.0596 MB) Zlib enabled. Server Time: 2019-07-21 21:28:57 UTC