ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
"Esoteric" countries and their wiring practices?
by Texas_Ranger. 04/20/19 07:00 PM
Norwegian power?
by Texas_Ranger. 04/20/19 06:27 PM
Welded Copper Connections
by gfretwell. 04/19/19 04:46 PM
Israel
by annemarie1. 04/18/19 02:35 PM
Water heater calculationsSo when I count calculati
by watersparkfalls. 04/13/19 12:43 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 12 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
art 630 #93751
06/08/05 11:59 PM
06/08/05 11:59 PM
O
OreElect  Offline OP
Member
Joined: Mar 2004
Posts: 98
Salem,Oregon.USA
Hi all.
Question for load calculation.
Ive got 2- 50 amp 480 volt 1 ph 70% duty welders.
Using the multiplier .84 for the 70 % duty cycle, I am to use this on the first 2 welders correct?
Also,if using a 3rd welder,using the 85 %,is this 85% of the .84 multiplier.
Your opinions appreciated

2017 / 2014 NEC & Related Books and Study Guides
Re: art 630 #93752
06/09/05 01:45 AM
06/09/05 01:45 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,348
Estero,Fl,usa
That's the way 630.11(B) reads to me

(B) Group of Welders. Conductor ampacity shall be based on the individual currents determined in 630.11(A) as the sum of 100 percent of the two largest welders, plus 85 percent of the third largest welder...


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,531 Are you busy
190,768 Re: Forum
180,490 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.004s) Memory: 0.9421 MB (Peak: 1.0591 MB) Zlib enabled. Server Time: 2019-04-22 16:26:27 UTC