SEU Cable #93373
05/19/05 08:46 PM
05/19/05 08:46 PM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,493
Michigan USA
Since we are required to use conductors suitable as sunlight resistant, are the conductors inside SEU cable meeting that requirement and usable as a cable riser for Service Entrance conductors? Must it say "Sunlight Reasistant" on the conductors?


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: SEU Cable #93374
05/19/05 09:02 PM
05/19/05 09:02 PM
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Page 40 UL Wire and Cable Marking Guide

Quote
SERVICE ENTRANCE CABLE (TYLZ)

GENERAL

This category covers service entrance cable designated Type SE and Type USE for use in
accordance with Article 338 of ANSI/NFPA 70, “National Electrical Code” (NEC).

Service entrance cable, rated 600 V, is Listed in sizes 14 AWG and larger for copper, and 12 AWG and larger for aluminum or copper-clad aluminum. Type SE cable contains Type RHW, RHW-2, XHHW, XHHW-2, THWN or THWN-2 conductors. Type USE cable contains conductors with insulation
equivalent to RHW or XHHW. Type USE-2 contains insulation equivalent to RHW-2 or XHHW-2 and is rated 90°C wet or dry.

The cable is designated as follows:

Type SE — Indicates cable for aboveground installation. Both the individual insulated conductors and the outer jacket or finish of Type SE are suitable for use where exposed to sun.

Types USE and USE-2 — Indicates cable for underground installation including direct burial in the earth. Cable in sizes 4/0 AWG and smaller and having all conductors insulated is suitable for all of the
underground uses for which Type UF cable is permitted by the NEC. Types USE and USE-2 are not suitable for use in premises or aboveground except to terminate at the service equipment or metering equipment.

Both the insulation and the outer covering, when used, on single and multiconductor Types
USE and USE-2, are suitable for use where exposed to sun.


Joe Tedesco, NEC Consultant
Re: SEU Cable #93375
05/19/05 11:03 PM
05/19/05 11:03 PM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,493
Michigan USA
Thanks Joe.


George Little

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 69
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,500 Are you busy
190,729 Re: Forum
180,459 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.004s) Memory: 0.9515 MB (Peak: 1.0751 MB) Zlib enabled. Server Time: 2019-04-20 22:57:14 UTC