antenna grounding #93282
05/11/05 09:37 PM
05/11/05 09:37 PM
S
stamcon  Offline OP
Member
Joined: Mar 2001
Posts: 333
So San Francisco CA
Has there been changes made to 810-21(99NEC)Grounding Conductors-Receiving Stations in the 2002 or 2005 NEC?

steve


Steve
2017 / 2014 NEC & Related Books and Study Guides
Re: antenna grounding #93283
05/15/05 08:15 PM
05/15/05 08:15 PM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
(F) Electrode. The grounding conductor shall be connected as follows:

(1) To the nearest accessible location on the following:
a. The building or structure grounding electrode system as covered in 250.50
b. The grounded interior metal water piping systems, within 1.52 m (5 ft) from its point of entrance to the building, as covered in 250.52
c. The power service accessible means external to the building, as covered in 250.94

d. The metallic power service raceway
e. The service equipment enclosure, or
f. The grounding electrode conductor or the grounding electrode conductor metal enclosures; or

(2) If the building or structure served has no grounding means, as described in 810.21(F)(1), to any one of the individual electrodes described in 250.52; or

(3) If the building or structure served has no grounding means, as described in 810.21(F)(1) or (F)(2), to an effectively grounded metal structure or to any of the individual electrodes described in 250.52.

[This message has been edited by Larry Fine (edited 05-15-2005).]

Oops! The italicized parts are the only changes.
Oops again; the above is from the '02 NEC.

[This message has been edited by Larry Fine (edited 05-15-2005).]

[This message has been edited by Larry Fine (edited 05-15-2005).]


Larry Fine
Fine Electric Co.
fineelectricco.com

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 2
Khombo 2
Popular Topics(Views)
255,836 Are you busy
191,816 Re: Forum
181,580 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.004s) Memory: 0.9434 MB (Peak: 1.0612 MB) Zlib enabled. Server Time: 2019-06-24 13:59:33 UTC