#93282 05/11/05 09:37 PM
Joined: Mar 2001
Posts: 333
S
stamcon Offline OP
Member
Has there been changes made to 810-21(99NEC)Grounding Conductors-Receiving Stations in the 2002 or 2005 NEC?

steve


Steve
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#93283 05/15/05 08:15 PM
Joined: Feb 2005
Posts: 693
L
Member
(F) Electrode. The grounding conductor shall be connected as follows:

(1) To the nearest accessible location on the following:
a. The building or structure grounding electrode system as covered in 250.50
b. The grounded interior metal water piping systems, within 1.52 m (5 ft) from its point of entrance to the building, as covered in 250.52
c. The power service accessible means external to the building, as covered in 250.94

d. The metallic power service raceway
e. The service equipment enclosure, or
f. The grounding electrode conductor or the grounding electrode conductor metal enclosures; or

(2) If the building or structure served has no grounding means, as described in 810.21(F)(1), to any one of the individual electrodes described in 250.52; or

(3) If the building or structure served has no grounding means, as described in 810.21(F)(1) or (F)(2), to an effectively grounded metal structure or to any of the individual electrodes described in 250.52.

[This message has been edited by Larry Fine (edited 05-15-2005).]

Oops! The italicized parts are the only changes.
Oops again; the above is from the '02 NEC.

[This message has been edited by Larry Fine (edited 05-15-2005).]

[This message has been edited by Larry Fine (edited 05-15-2005).]


Larry Fine
Fine Electric Co.
fineelectricco.com

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 187
Joined: November 2005
Top Posters(30 Days)
triple 3
grich 2
dobler 2
Asset 2
Popular Topics(Views)
293,084 Are you busy
225,069 Re: Forum
210,491 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5