If I want to run 2 circuits to a detached building in the residential setting, do I have to install a sub panel? I say you do???
George Little
|
|
|
|
Joined: Jul 2004
Posts: 9,992 Likes: 35
Member
|
You can run a single multiwire feeding 2 120v legs but not 2 separate circuits ... the way I see it.
Greg Fretwell
|
|
|
|
Joined: Mar 2003
Posts: 849
Member
|
Wouldn't 225.36 Exception Apply.
|
|
|
|
Joined: Jan 2004
Posts: 1,507
OP
Member
|
Ernie- 225.30 limit's you to one supply with additional supplies for special conditions and residential homes can't qualify for any of these special conditions. So at best we could run a multiwire branch circuit and call it one circuit like Greg says. And I agree.
George Little
|
|
|
|
Joined: Jul 2004
Posts: 9,992 Likes: 35
Member
|
I think the real intent is that all remote buildings get a panel, ground etc like an "HO guage service" but they make an exception for the guy who just wants a light and a receptacle in his shed. It probably makes a few less orange cords strung through the trees.
Greg Fretwell
|
|
|
|
Joined: Jul 2004
Posts: 9,992 Likes: 35
Member
|
Now the obligatory "gee whiz" question. If the feeder is #10/3wg with a 30a sub panel, what size wire do you run to the ground rod?
Greg Fretwell
|
|
|
|
Joined: Jan 2004
Posts: 1,507
OP
Member
|
And the "obligatory" answer is minimum #8 cu. I liked that word"obligatory" so I thought I'd use it in the answer, must be the inspector in me. Could use #6 AL if you could figure out some way to keep it 18" above the earth.
George Little
|
|
|
|
Joined: Feb 2004
Posts: 133
Member
|
Do you think Table 250.66 note 2 might allow you to use a #10 here ? Using the argument that the feeders to the subpanel are not Service Entrance Conductors and thus the "equivalent" size service entrance conductors to feed the load would be (is, in fact) #10.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
How about if I connect the two structures with a fence?
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Feb 2004
Posts: 133
Member
|
I don't think the fence can make a difference. If joining 2 structures with a fence creates a single structure than I live in my neighbors house. Or does he live in mine
|
|
|
Posts: 7,400
Joined: April 2002
|
|
|
|
|