#93164 05/05/05 08:13 PM
Joined: Feb 2003
Posts: 687
A
Member
I looked at a house with a strange set up with the service. The service drop is overhead about 20' to the garage. On the back of the garage is the mast and meter. Inside is a 100a fused disco. Then the load side gos underground in 2" about 30' to the house load center.

I can't find anything in the NEC about this. I keep thinking I read it's not permited some where but maybe I'm thinking of a local thing some place.

They are doing an addition so a larger service will be needed. If keeping with a simular set up what would the proper way to bond and ground? I would say a G-rod at the house and garage plus cold water at the house. Bond only the disco & meter at the garage and pull a EG to the house panel. The house panel would have a insulated nutral bar.

I would proibly just use a meter socket with a built in ocp.

Right now the garage circuit is just double taped of the load side of the disco and gos to a single 20a breaker. Could I just put it on a breaker in the house and run the garage circuit with the house feeders?

Tom
Tom

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member
What's the question? The house has a sub panel, the garage is the main building with the service disconnect. Whether you need a 3 wire or 4 wire feeder (reground the neutral etc) depends on if there are other metalic paths. You do need a ground electrode system at both buildings.


Greg Fretwell
Joined: Feb 2003
Posts: 687
A
Member
Sorry for not being to the point.

Can the house have a sub panel with the service in a detached garage?

Tom

Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member
That is not unusual. It is an easy way to increase the service size for a garage shop when the house service was OK. The NEC is silent on which building the service disconnect needs to be in/on.


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 99
Joined: August 2003
Top Posters(30 Days)
BigB 7
triple 3
Popular Topics(Views)
302,738 Are you busy
231,967 Re: Forum
216,685 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5