Joined: Jan 2002
Posts: 1,457
E
Member
Looking for some info regarding panel size. Example residential 200 amp service feeding three apartments and a landlord panel. What size panels? Where in the book is there info on exceeding sevice conductor ratings?
Thanks, Scott

Horizontal Ad
Joined: Dec 2000
Posts: 4,293
Member
If you're going by '02 Code, try Table 310.15(B)(6).
Your load will be determined by the usual calculation methods.

Joined: Mar 2001
Posts: 2,056
R
Member
'02 Code.
230.80
230.90(A) Exception 3.
The service conductors need to be adequate for the calculated load.
But, the combined rating of "up to six service disconnects" is allowed to exceed the SE conductors ampacity as long as any individual disconnect is adequately sized for the load it serves.

Scott,
I'm not sure this is what you're asking, but the NEC Handbook details the principal described above.


Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
Admin
Admin
NY, USA
Posts: 3,672
Joined: October 2000
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
556,944 Are you busy
431,755 Re: Forum
401,133 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5