Taps to branch circuits? #92964 04/21/05 08:22 AM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline OP
Member
Would it be proper to tap a 20a circuit at each outlet with a short (6 inch) piece of #14 wire to install a duplex 15a receptacle? I seem to remember a discussion on this before but can't find the code reference. Only thing I find is 210.19(A)(4)(c) and it says "No" Comments please.


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Taps to branch circuits? #92965 04/21/05 08:37 AM
Joined: Jun 2004
Posts: 613
S
shortcircuit Offline
Member
240.4(D) restricts #14 to be connected to a 15 amp overcurrent device...

Now, there are exceptions to this rule, but as you pointed out, 210.19(4) exception No. 1(c) spells out the restriction of taps connected to receptacle outlets...

shortcircuit

Re: Taps to branch circuits? #92966 04/21/05 01:09 PM
Joined: Jul 2004
Posts: 9,532
G
gfretwell Offline
Member
There is an exception for lamp holders and luminaires but I don't think that extends to a receptacle. Receptacles are the reason for 240.4(D) in the first place IMHO. The installer has no control over what a user does so they build the 80% safety factor into the installation.


Greg Fretwell
Re: Taps to branch circuits? #92967 04/21/05 10:52 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Code is pretty blunt in saying that you can't do this with receptacles...you can put 15 amp receptacles on a 20 amp circuit, but you can't pigtail with #14- even though general tap rules would otherwise allow it.

I, for one, do not understand why code denies this practice. Are they trying to prevent the use of cheap 'back-stab' receptacles on 20 amp circuits? Your guess is as good as anyones'.

Re: Taps to branch circuits? #92968 06/23/05 09:50 PM
Joined: May 2004
Posts: 11
J
JimMichaels Offline
Member
It would seem reasonable for a single 15a receptacle ... until a cube tap gets plugged in. A duplex would need dual 15a taps. Hence, NO!

Re: Taps to branch circuits? #92969 06/24/05 11:58 AM
Joined: Jul 2004
Posts: 9,532
G
gfretwell Offline
Member
In George's question he implied that all of this tap would be inside a box so the hazard is probably not there but it is still a <technical> code violation. If this was simply to pigtail in a receptacle I doubt anyone would ever actually have any problems.


Greg Fretwell

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,722 Are you busy
204,962 Re: Forum
193,067 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3