Is NM wire legal in a home through studs that may not be drywalled? Such as under a loft floor you can walk under?
Years ago in Michigan, we used to run NM inside residential unattached garages inside the stud walls with no drywall going on them, and it was legal. They always passed inspection. (wonder if thats still legal?)


The Golden Rule - "The man with the gold makes the rule"
Horizontal Ad
#92592 03/28/05 12:24 PM
Joined: Feb 2005
Posts: 361
C
Member
Have you checked 334.23 (and 320.23)?


~~ CELTIC ~~
...-= NJ =-...
#92593 03/28/05 01:42 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Article 334 Section 334.10(A)(1) permits this type of installation.


George Little
#92594 03/28/05 02:09 PM
Joined: Feb 2002
Posts: 840
C
Member
This is very common in New England. Standard practice.


Peter
#92595 03/28/05 10:11 PM
Joined: Jan 2004
Posts: 1,507
G
Member
I seem to remember a subject that came up as an IAEI code panel question and it pertained to the use of NM cable run exposed and terminated in nonmetallic boxes. The issue was the boxes and their suitability for use in the walls when they were not drywalled. Anybody had any issus with that?


George Little
#92596 03/29/05 04:53 PM
Joined: Apr 2004
Posts: 60
M
Member
Are these code references from 2005 and different from 2002? They don't seem real relevant to the issue. To me, the problem lies in 334.14(B) Exposed Work, Protection from physical damage, and 300.4 (which covers some of the protection issues).

What is subject to physical damage is up to the inspector to determine. I too have seen many garages wired with NM run between the studs with no further protection from damage (but these were installed 20 to 30 years ago).


Mark
Kent, WA
#92597 03/30/05 02:05 AM
Joined: Nov 2002
Posts: 794
Likes: 3
W
Member
People have been known to store tools like rakes and shovels in such a way that the romex keeps the tools from falling over. Where the romex was strung horizontally thru holes in studs about 4 feet above the floor. Can't be good for the wire or the safety of the home owner.

[This message has been edited by wa2ise (edited 03-30-2005).]

Horizontal Ad
#92598 03/30/05 06:49 AM
Joined: Mar 2005
Posts: 8
R
Junior Member
The AHJ in our area permits this type of installation in areas not sheetrocked. They do however require that in those areas such as garages where the romex is run horizontal that a protective wooden strip be nailed up in front of the romex referencing (sp?) 334.14 (b). We normally run the romex vertical along the stud, through the top plate and back down at the next location thus avoiding any questions and overall a neater installation.

#92599 03/30/05 07:36 AM
Joined: Jan 2004
Posts: 1,507
G
Member
You have a similar situation in basements when the NM cable is run in the floor joist for the first floor. People hang thing on the NM cable like clothes hangers for example. Running furring strips on the bottom side of the joist and stapling the NM cable to the bottom side of the furring strips would solve that. Contractors don't won't do that because it's to labor intensive. I'd like to do it just once and see some "green" inspector try and write a violation [Linked Image]


George Little
#92600 03/30/05 10:37 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Yes, hard to believe its legal to run through floor joist in basements without a finished ceiling.


The Golden Rule - "The man with the gold makes the rule"

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Posts: 362
Joined: April 2003
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
337,240 Are you busy
262,772 Re: Forum
243,070 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5