Grouding conductor on 4000 amp service #92582
03/27/05 01:19 PM
03/27/05 01:19 PM
K
kenny2656  Offline OP
Junior Member
Joined: Mar 2004
Posts: 7
lake charles, la usa
I am currently working on a theater with a 4KA service. Service conductors from pad mount transformer = 8 sets 4 conductors 750MCM. After consulting table 250.66 and the following notes,
I am confused on how to determine the grounding electrode conductor.The EE calls for 250MCM copper. Is this correct?

2017 / 2014 NEC & Related Books and Study Guides
Re: Grouding conductor on 4000 amp service #92583
03/27/05 02:41 PM
03/27/05 02:41 PM
G
Gregtaylor  Offline
Member
Joined: Mar 2005
Posts: 212
Boise, Idaho, USA
According to 250.66 it would be 3/0 copper or 250 MCM alum/copper clad alum. I don't see where there could be an argument for 250 copper UNLESS THE ENGINEER SPEC'D IT!! Since you said it was the EE, he gets to specify. They love to oversize stuff.

Re: Grouding conductor on 4000 amp service #92584
03/27/05 03:14 PM
03/27/05 03:14 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I agree that 250 copper is larger than required by the NEC for the service conductors you have.

That said there is no problem with oversize conductors as long as you picked that up on the bid.

The higher the job cost the more profit you should make. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Grouding conductor on 4000 amp service #92585
03/30/05 12:21 PM
03/30/05 12:21 PM
G
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
Using a larger cable than is necessary will also create a choke. It actually slows down the reaction to ground (when you want a fault to follow a wide dispersion pattern). This may be the case where you are working... or may not, sometimes people do stuff that does not make sense and appreciate you asking, sometimes they are offended, how's your relationship with the EE?

Just something to consider.

Re: Grouding conductor on 4000 amp service #92586
03/30/05 12:44 PM
03/30/05 12:44 PM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 849
Michigan
750 mcm 75% on 310.16= 475 amps
475x 8=3800amps
Read 240.4c over 800amps wire size MUST be equal to OR greater then. Also Read 220.22 about Neutral size ,You might be able to Dn. size it.
Grounding Electrode conductor Sizes per 250.66 3/0 Minumum.

Re: Grouding conductor on 4000 amp service #92587
04/03/05 11:57 AM
04/03/05 11:57 AM
K
kenny2656  Offline OP
Junior Member
Joined: Mar 2004
Posts: 7
lake charles, la usa
Service actually consists of (1) 2500 amp CB, (1)1600 amp CB and (2) 100 amp CB so the 8 sets of 750MCM is not based on a 4KA main breaker. Sorry I should have stated that in my original post.I will check into downsizing the neutral, but I doubt the EE will allow it without a deduct.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
257,104 Are you busy
192,936 Re: Forum
182,593 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.003s) Memory: 0.9768 MB (Peak: 1.1234 MB) Zlib enabled. Server Time: 2019-07-19 08:34:57 UTC