ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
How's Florida doing with Hurricane Ian?
by Bill Addiss - 09/28/22 12:41 PM
Tough being a lineman's kid
by Bill Addiss - 09/28/22 12:39 PM
GFCI's pops in large numbers
by dsk - 09/26/22 04:35 AM
AFCI’s Revisited
by sparky - 09/24/22 09:58 AM
NFPA Price Increase Coming
by Bill Addiss - 09/23/22 02:22 PM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 25 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Mar 2004
Posts: 7
K
Junior Member
I am currently working on a theater with a 4KA service. Service conductors from pad mount transformer = 8 sets 4 conductors 750MCM. After consulting table 250.66 and the following notes,
I am confused on how to determine the grounding electrode conductor.The EE calls for 250MCM copper. Is this correct?

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Mar 2005
Posts: 212
G
Member
According to 250.66 it would be 3/0 copper or 250 MCM alum/copper clad alum. I don't see where there could be an argument for 250 copper UNLESS THE ENGINEER SPEC'D IT!! Since you said it was the EE, he gets to specify. They love to oversize stuff.

Joined: Jan 2003
Posts: 4,391
I
Moderator
I agree that 250 copper is larger than required by the NEC for the service conductors you have.

That said there is no problem with oversize conductors as long as you picked that up on the bid.

The higher the job cost the more profit you should make. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: May 2001
Posts: 717
G
Member
Using a larger cable than is necessary will also create a choke. It actually slows down the reaction to ground (when you want a fault to follow a wide dispersion pattern). This may be the case where you are working... or may not, sometimes people do stuff that does not make sense and appreciate you asking, sometimes they are offended, how's your relationship with the EE?

Just something to consider.

Joined: Mar 2003
Posts: 849
Y
Member
750 mcm 75% on 310.16= 475 amps
475x 8=3800amps
Read 240.4c over 800amps wire size MUST be equal to OR greater then. Also Read 220.22 about Neutral size ,You might be able to Dn. size it.
Grounding Electrode conductor Sizes per 250.66 3/0 Minumum.

Joined: Mar 2004
Posts: 7
K
Junior Member
Service actually consists of (1) 2500 amp CB, (1)1600 amp CB and (2) 100 amp CB so the 8 sets of 750MCM is not based on a 4KA main breaker. Sorry I should have stated that in my original post.I will check into downsizing the neutral, but I doubt the EE will allow it without a deduct.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Top Posters(30 Days)
Popular Topics(Views)
297,694 Are you busy
228,493 Re: Forum
213,326 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5