AFCI #92567
03/26/05 02:23 PM
03/26/05 02:23 PM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 233
Washington...Not DC
would an AFI work, if you had a back up power (5kw generator) feeding the breaker?

The breaker would be fed through a manual transfer switch, one side of the switch from
the AFI and the other from the generator.

It seems like the breaker would be an intergal part of the neutral since the banch circuit is landed in it and then bonded to the nutral busbar. And if the breaker is de-energized would it be an open circuit when the generator tries to feed it?

Any thoughts would be appreciated.
Thanks.

2017 / 2014 NEC & Related Books and Study Guides
Re: AFCI #92568
03/27/05 01:42 PM
03/27/05 01:42 PM
T
tdhorne  Offline
Member
Joined: Mar 2001
Posts: 345
Maryland, USA
Use a double pole double throw transfer switch and it will be a non issue. If you transfer both the neutral and the hot the generator functions as a derived system. The easiest way to provide grounding will depend on how your generator is configured. If its neutral is bonded to the frame then you will need to run a Grounding Electrode Conductor (GEC) from your house's grounding electrode system to the bonding lug on your generator. If the generator neutral is not bonded to the generator frame then it will be easier to bond the neutral to ground in the transfer switch and run the GEC to the grounding electrode system from the switch's enclosure.
--
Tom H


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Re: AFCI #92569
03/27/05 10:10 PM
03/27/05 10:10 PM
P
pdh  Offline
Member
Joined: Jan 2005
Posts: 354
How do you intend to comply with 210.12 during the time the generator is supplying power?

Re: AFCI #92570
03/28/05 01:55 AM
03/28/05 01:55 AM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 233
Washington...Not DC
well 702.3 is specific.
the only thing left is to get a blessing from the "ahj" and filling out a proposal to the panel for an exception here.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
256,961 Are you busy
192,847 Re: Forum
182,460 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.9591 MB (Peak: 1.0905 MB) Zlib enabled. Server Time: 2019-07-16 00:46:40 UTC