#92545 03/22/05 11:46 PM
Joined: Mar 2004
Posts: 814
B
BigB Offline OP
Member
I realize AFCI protection is required at all bedroom outlets including the smoke but I have a situation where the whole bedroom is on one circuit, then there is a two gang box by the patio door. In this two gang box there is a three way for the bedroom light and a four way which switches the patio lighting which is on a different circuit. Would this be a violation? Should the patio circuit now also be AFCI protected because this one switch's wiring enters the bedroom 2 gang?

By the way didn't there used to be an AFCI forum?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jan 2005
Posts: 354
P
pdh Offline
Member
Quote
210.12(B) Dwelling Unit Bedrooms. All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit bedrooms shall be protected ...

What I read here is that this is protection required of the circuit itself (not of just the outlet), if the circuit is supplying an outlet installed in a bedroom. So is your 4-way switch considered an outlet? Is the patio light considered installed in the bedroom?

Joined: Dec 2004
Posts: 209
H
Member
The way I see it is a switch is not an outlet by the definitions (Article 100) in the NEC. An outlet is "a point on the wiring system at which current is taken to supply utilization equipment". A switch is "a device...capable of interrupting its rated current at its rated voltage". It is not the point at which current is taken to supply utilization equipment...IMO.
Harold

Joined: May 2002
Posts: 1,716
R
Member
I agree, the switch (which is not an outlet) for a circuit serving outlets outside of the bedroom would not be an issue.

This can be expanded into allowing 125v non AFCI 15 and 20 amp breakers in a panel or enclosure to be installed in the bedroom. [Linked Image]

Roger

[This message has been edited by Roger (edited 03-23-2005).]

Joined: Mar 2004
Posts: 814
B
BigB Offline OP
Member
Thanks a heap guys.