what is the requirement (wire size) for bonding the copper water pipe when it comes in as a poly pipeand changes over to copper?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#92487 03/17/05 10:25 PM
Joined: Jun 2004
Posts: 613
S
Member
Follow the rules of table 250.66 as instructed by 250.104(A)(1)2005NEC