Generator remote from building ,has disconnect switch on it. Runs to building inside to Transfer Switch. Is a Additional Disconnect switch Required per Article 225.As the Generator feeders enter the building and before the Transfer switch?

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Jun 2004
Posts: 613
S
Member
whatsup yoopersup...I say yes to your question, and it must be suitable for service equipment.

Unless the transfer equipment meets the qualifications of Article 225...

shortcircuit

Joined: Mar 2003
Posts: 849
Y
Member
Found the Answer ,700.12B(6)Was added in the 2002 Code. take a look.