Main Disconnect #92395 03/15/05 02:57 PM
Joined: Oct 2004
Posts: 51
I
InspectorE Offline OP
Member
Situation: Home plus agricultural building, current service is 200 amp.

The service line comes into a central point which is a generator shed (that's where the meter is). There is currently a 200 amp disconnect at the shed. Originally, the 200 amp was to feed both the house and the pole barn but now it is desired to upgrade to 300 amp service so the pole barn can have it's own 100 amp capacity leaving the full 200 amps for the home.

Can I just add a second 100 amp disconnect switch for the separate pole barn, or must I purchase a 300 amp disconnect so both buildings can be disconnected with a single switch? I realize a new meter socket will be necessary. I can't find anything specific in the code, but it may be inferred by a few sections.

Thanks!

2017 / 2014 NEC & Related Books and Study Guides
Re: Main Disconnect #92396 03/15/05 08:57 PM
Joined: Dec 2003
Posts: 751
E
earlydean Offline
Member
It is OK to just add a 100 amp disconnect for the shed. You are allowed up to six disconnects per service (230.71). The riser or lateral (and the meter enclosure) would need to be adequate for 300 amps if the load calculations warranted it, but, you could then tap off to each disconnect with 200 amp and 100 amp taps for the two buildings. What feeds the shed?

By the way, each building needs its own disconnect.

2002 NEC:
"VI. Service Equipment — Disconnecting Means
230.70 General.
Means shall be provided to disconnect all
conductors in a building or other structure from the service entrance conductors.
(A) Location. The service disconnecting means shall be installed in accordance with 230.70(A)(1), (2), and (3).
(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors."

I infer from your description that the service conductors stop at the shed, and feeders will feed each building.

"225.31 Disconnecting Means.
Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.
225.32 Location.
The disconnecting means shall be installed either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors."

How close is that generator shed? Sounds like you need additional disconnects at each building.


Earl

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Admin 1
Popular Topics(Views)
270,686 Are you busy
204,927 Re: Forum
193,041 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3