ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Ground Rods: Installation and Hook-Up
by renosteinke - 11/26/22 07:28 PM
Happy Thanksgiving all!
by Bill Addiss - 11/24/22 08:37 AM
Colt Firearms Switchbox
by sabrown - 11/22/22 01:33 PM
Perfect work light?
by gfretwell - 11/22/22 12:48 AM
copper prices where you live and inflation
by gfretwell - 11/21/22 01:52 PM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 18 guests, and 47 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#92395 03/15/05 01:57 PM
Joined: Oct 2004
Posts: 55
I
Member
Situation: Home plus agricultural building, current service is 200 amp.

The service line comes into a central point which is a generator shed (that's where the meter is). There is currently a 200 amp disconnect at the shed. Originally, the 200 amp was to feed both the house and the pole barn but now it is desired to upgrade to 300 amp service so the pole barn can have it's own 100 amp capacity leaving the full 200 amps for the home.

Can I just add a second 100 amp disconnect switch for the separate pole barn, or must I purchase a 300 amp disconnect so both buildings can be disconnected with a single switch? I realize a new meter socket will be necessary. I can't find anything specific in the code, but it may be inferred by a few sections.

Thanks!

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#92396 03/15/05 07:57 PM
Joined: Dec 2003
Posts: 751
E
Member
It is OK to just add a 100 amp disconnect for the shed. You are allowed up to six disconnects per service (230.71). The riser or lateral (and the meter enclosure) would need to be adequate for 300 amps if the load calculations warranted it, but, you could then tap off to each disconnect with 200 amp and 100 amp taps for the two buildings. What feeds the shed?

By the way, each building needs its own disconnect.

2002 NEC:
"VI. Service Equipment — Disconnecting Means
230.70 General.
Means shall be provided to disconnect all
conductors in a building or other structure from the service entrance conductors.
(A) Location. The service disconnecting means shall be installed in accordance with 230.70(A)(1), (2), and (3).
(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors."

I infer from your description that the service conductors stop at the shed, and feeders will feed each building.

"225.31 Disconnecting Means.
Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.
225.32 Location.
The disconnecting means shall be installed either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors."

How close is that generator shed? Sounds like you need additional disconnects at each building.


Earl

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Top Posters(30 Days)
NORCAL 3
Trumpy 3
Popular Topics(Views)
300,203 Are you busy
229,934 Re: Forum
214,773 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5