ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
How's all our Non-US folks doing?
by djk - 07/23/21 09:13 PM
Switched Receptacles -Top or Bottom?
by donles - 07/23/21 10:51 AM
Do You Travel?
by Bill Addiss - 07/20/21 04:26 PM
Backup Generator Done Right
by timmp - 07/18/21 12:20 PM
Square D "All-In-One" Panelboard
by Rachel - 07/16/21 04:57 AM
New in the Gallery:
OOPSIE!
OOPSIE!
by timmp, July 13
AT&T Office Thermostat, Summer
AT&T Office Thermostat, Summer
by timmp, July 13
Who's Online Now
0 members (), 27 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#92369 03/14/05 10:54 PM
Joined: Oct 2002
Posts: 830
S
Member
I must be missing something. When I calculate a 30 hp. motor on 460 volts @ 40 amps, using an inverse time breaker, I get:
40 amps X 250 % = 100 amps. I just looked in my "Uglies Electrical References" book, and they calculate it as being a 70 amp. breaker. Any idea what's going on. I have a 400 amp. panel I'm getting ready to order, and I have to have the breaker sizes ready to order it. I don't want to order the wrong size breakers [Linked Image] Pretty expensive mistake. Does not 430-52 allow me to go up to the next higher rated breaker if my calculations do not correspond to a standard size?? In this particular case, 100 amp. is a standard size, but I have other ones that will not be. I figure " Ugly is probably right, but where am I going wrong?? I can't afford to calculate this job wrong. Thanks again... Steve

2017 / 2014 NEC & Related Books and Study Guides
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
It looks like your caculations are correct.
The 100 amp is the max size breaker you can use. You may not go up the the next size.
You may go to an 80 amp breaker if it will
allow the motor to start.
i don't know why Uglys would list a 70 amp.
That seems to be too small.

Joined: Feb 2004
Posts: 133
E
Member
430.52(C)(1) Exception 1 allows going to the next higher size the way I read it.

Exception No. 1: Where the values for branch-circuit short-circuit and ground-fault protective devices determined by Table 430.52 do not correspond to the standard sizes or ratings of fuses, nonadjustable circuit breakers,thermal protective devices, or possible settings of adjustable circuit breakers, a higher size, rating, or possible setting that does not exceed the next higher standard ampere rating shall be permitted.

Joined: Apr 2004
Posts: 156
R
Member
Table 430-152 lists the maximum setting of 250%. This can be changed per 430-52(c)(1)(c)to 400% for loads of 100A or less. I think Uglies is looking at the breaker as disconnecting means per 430-110. This gives a minimum 115%. Where I work we use mimimum 150% on motor circuit breakers with a maximum of 400%. I think the only other consideration would be given to the locked rotor amp rating.

Still, 150% of 40 would be a 60 amp breaker. Are they using 175%? I can't think of any reason in particular they would use that. Edit from here, I looked at the wrong column.

[This message has been edited by rad74ss (edited 03-16-2005).]


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Top Posters(30 Days)
timmp 4
Rachel 4
Popular Topics(Views)
281,407 Are you busy
215,050 Re: Forum
201,934 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5