If a circuit supplies a fluorescent, mercury or metal halide do the neutrals still have to be counted as current carrying? This neutral will carry a third harmonic.
Thanks for any replies
Greg
|
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Yes, any non-linear(harmonic) load creates a current carrying nuetral.
Ryan Jackson, Salt Lake City
|
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
Only on 3 phase systems. Don
Don(resqcapt19)
|
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
... and only when that nonlinear load is the major portion (over 50%) ....
See the 2005 NEC .....
Nonlinear Load. A load where the wave shape of the steady-state current does not follow the wave shape of the applied voltage.
Article 310
(c) On a 4-wire, 3-phase wye circuit where the major portion of the load consists of nonlinear loads, harmonic currents are present in the neutral conductor; the neutral shall therefore be considered a current-carrying conductor. FPN: Electronic equipment, electronic/electric-discharge lighting, adjustable-speed drive systems, and similar equipment may be nonlinear loads.
Joe Tedesco, NEC Consultant
|
|
|
|
|
Joined: Jul 2004
Posts: 10,026 Likes: 37
Member
|
You can still induce out of phase currents in a single phase neutral (multiwire circuit) but you won't get the overload effect you get in 3 phase. It can still make measurememnts not balance if your meter isn't true RMS.