Well casing cap #92134
02/26/05 11:58 PM
02/26/05 11:58 PM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,493
Michigan USA
What is the best way to ground/bond the metal cap found on the top of some well casings? Some of the casings (about 50%) are non metallic with a metal cap that could become energized.


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Well casing cap #92135
02/27/05 06:20 AM
02/27/05 06:20 AM
S
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 610
massachusetts
george...thought we determined that isolated sections of steel need not be bonded [Linked Image]

How about braided bonding jumper to the cap terminating to a lug bolted to a tapped 1/4-20 hole in the cover.

It would be better if they used a non-metalic cover with the non-metalic casing IMO.Haven't seen other than metel casings around these parts.

While were on the subject of wells, do the installations that you see have a disconnect at the casing for servicing the pump?

Most of the installations around here have no disconnect at the casing for the pump motor down in the casing and the wiring extends inside the dwelling to a location where a storage tank is, then through the pressure switch, then to the breaker in the service. The breaker at the service being the only disconnect for the installation.Wouldn't this be a violation of 430.102(B)

shortcircuit

Re: Well casing cap #92136
02/27/05 09:26 AM
02/27/05 09:26 AM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,493
Michigan USA
430.102(B) Exception (c) uses the word "impracticable" and the definition is impossible, infeasible, unattainable and words like that. So certainly the motor at the bottom of the well fits that exception with respect to locating a disconnect "within sight"


George Little
Re: Well casing cap #92137
02/27/05 09:32 AM
02/27/05 09:32 AM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,493
Michigan USA
More on well casings: There is concerns about the well cap being energized because there is a splice right there and usually the well driller makes that splice and one can only hope he has the right talent and materials to make a good splice. I'm also hearing that there is a lug on the underside of this cap with a green screw that should be utilized,


George Little
Re: Well casing cap #92138
02/27/05 12:04 PM
02/27/05 12:04 PM
S
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 610
massachusetts
IMO...I don't see how locating a disconnect next to the well casing is "impracticable" and would be as close as you can practically get to being in sight of the pump. It would definitely lessen the hazard to service personal from somebody accidentally turning the power on at the panel.

There should be at least provisions to lock the circuit in the open position. Wait a minute...code already says that.

Well to get back on track of your original concern of the metalic well casing cap, I have seen some caps with the ground lug or screw as you describe.

shortcircuit

Re: Well casing cap #92139
02/27/05 07:29 PM
02/27/05 07:29 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,348
Estero,Fl,usa
I am not sure how they do wells there but here they have an FS box at the well head with a short piece of liquidtite going to the cap. When they "pull" the well they open the splice in that box and disconnect the liquidtite from the box.
I could have installed a disco in the box but I didn't see the point. There is one "in sight" tho in the pump shack about 10' away.


[Linked Image]

[This message has been edited by gfretwell (edited 02-27-2005).]


Greg Fretwell
Re: Well casing cap #92140
02/28/05 10:18 PM
02/28/05 10:18 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Greg,

They should just use a plastic bonding screw! (LOL) Actually most well casings I see here in NJ have the metal cap with a splice point ( and ground point) right underneath the cap. The well installer "SHOULD" install that ground wire. I will check for it on a Final inspection, but the well installer is usually gine by then. So the GC or EC will have to take care of that problem.

Re: Well casing cap #92141
02/28/05 10:42 PM
02/28/05 10:42 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,348
Estero,Fl,usa
I never saw an electrical inspector when they punched this well. The well inspector only cared that the well was "producing" and that the old well was capped (poured solid with concrete). If this had been a metal cap there was no reason it couldn't have been bonded to the EGC in the splice box.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,531 Are you busy
190,769 Re: Forum
180,492 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.028s Queries: 14 (0.004s) Memory: 0.9939 MB (Peak: 1.1535 MB) Zlib enabled. Server Time: 2019-04-22 18:55:38 UTC