Dryer receptacles - was this ever allowed? #91749 02/03/05 10:52 AM
Joined: Jan 2005
Posts: 18
B
BPiersel Offline OP
Member
Hello,

I recently bought an older house, and I have been finding problems with the wiring in the breezeway and garage that was added on in the 80’s. It appears to have been a lot of DIY work that never got inspected properly. The most recent one I have found is with the dryer receptacle. This is a 10-30R (3-wire) receptacle fed from a subpanel. I know that this is not allowed by 2002 NEC, but was the 3-wire receptacle ever allowed when fed from a subpanel? I thought it was only allowed when fed from the main panel, since neutral and ground are bonded together there. I’m just wondering if this may have been allowed by code when it was installed or if it is another example of incorrect wiring. I plan to replace it with a 14-30R, since the cable has 3 conductors plus the ground.

Brian

2017 / 2014 NEC & Related Books and Study Guides
Re: Dryer receptacles - was this ever allowed? #91750 02/03/05 01:01 PM
Joined: Jan 2002
Posts: 163
D
dana1028 Offline
Member
"but was the 3-wire receptacle ever allowed when fed from a subpanel? I thought it was only allowed when fed from the main panel"

3-wire receptacles (i.e. using the neutral to ground dryer frames) was permitted up until 1996 (?); they were permitted to originate in any panel as long as the neutral was insulated.

Quite freguently SE cable was used to wire up stoves, ovens, dryers. Some of this cable did not have an insulated grounded (neutral) conductor. You were not permitted to use this type cable inside a house unless: you were feeding stoves, ovens, dryers and the circuit originated in the service.

See 1979 - 250-60(C) & 338-3(b)

Re: Dryer receptacles - was this ever allowed? #91751 02/03/05 05:33 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
I was always told 3 wire range and dryer feeds where not permitted from sub panels, I will have to check my local amendments.

[This message has been edited by iwire (edited 02-03-2005).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Dryer receptacles - was this ever allowed? #91752 02/03/05 05:54 PM
Joined: Jan 2005
Posts: 9
M
mike d Offline
Junior Member
this was common, look at 250.140 (3) in the 2002 NEC applies to existing ranges & dryers, if the grounded conductor is uninsulated it must originate at the service
equipment, and also look at 250.42 (B) exception #1 permits load side grounding, on existing ranges & dryers,

Re: Dryer receptacles - was this ever allowed? #91753 02/06/05 09:39 AM
Joined: Apr 2004
Posts: 201
CharlieE Offline
Member
It was permitted to feed them from a distribution panelboard but it was not permitted to use SE cable from that location. You were required to use a cable with an insulated neutral. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
Re: Dryer receptacles - was this ever allowed? #91754 02/06/05 09:48 AM
Joined: May 2004
Posts: 162
C
cpal Offline
Member
My 1996 NEC in Article 250.60(c) States
The grounded conductor is insulated and part of Type SE service-entrance cable and the branch circuit originates at the service equipment.

This language was removed in the 99

Charlie

Re: Dryer receptacles - was this ever allowed? #91755 02/07/05 11:15 AM
Joined: Jan 2005
Posts: 18
B
BPiersel Offline OP
Member
Thanks for the info, everyone.

If the neutral has to be insulated from a subpanel, wouldn't there always be a separate grounding conductor in the cable, so you'd always end up running a total of 4 conductors from the subpanel? Since you'd always have the separate neutral and ground conductors, the only real reason to put a 3-wire receptacle fed from a subpanel would be to avoid changing the appliance cord, which I assume was the reason in this case.

Brian

Re: Dryer receptacles - was this ever allowed? #91756 02/07/05 12:26 PM
Joined: Jul 2004
Posts: 9,546
G
gfretwell Offline
Member
Long ago I asked why you would run 10-3/wg to a 3 prong dryer outlet and the answer was that since the 3d wire is identified as a groundED conductor <some AHJs said> it had to be white, even tho it was also used as a groundING conductor. They usually attached the bare wire to the backstrap of the receptacle and the white to the ground contact. Once "the war was over" it is easy to go to the 4 pronger.


Greg Fretwell

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 19
Popular Topics(Views)
272,182 Are you busy
206,068 Re: Forum
194,077 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3