#91517 01/20/05 06:32 PM
Joined: Jan 2003
Posts: 59
C
ccdave Offline OP
Member
a new cell site requiring its own metered service, fed off an 480/277 3ph 4wire BUT the new service panel is only providing 460 to a transformer on the roof, can that be done per code? It is a 3ph 4 wire service panel, neutral is for the meter and only 2 phases are being used--thanks

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#91518 01/25/05 10:59 PM
Joined: Mar 2001
Posts: 345
T
Member
Quote
ccdave a new cell site requiring its own metered service, fed off an 480/277 3phase 4wire BUT the new service panel is only providing 460 to a transformer on the roof, can that be done per code? It is a 3 phase 4 wire service panel, neutral is for the meter and only 2 phases are being used--thanks
"an 480/277 3 phase 4wire" WHAT? Is it a service, a switchboard, panel? Is the service panel in your posting the source of the feeder to the roof? When you say only two phases are being used may I conclude that you mean that the feeder will be single phase derived between two of the ungrounded conductors of the wye connected service panel? If the answer is yes than I see no problem. Single phase circuits, such as the circuit supplying the rooftop transformer, are run from three phase panels all the time.
--
Tom H


[This message has been edited by tdhorne (edited 01-25-2005).]


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Top Posters(30 Days)
BigB 4
triple 3
Popular Topics(Views)
303,070 Are you busy
232,137 Re: Forum
216,853 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5