ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Switched Receptacles -Top or Bottom?
by gfretwell - 07/28/21 10:06 PM
Lowes Selling this fan
by timmp - 07/25/21 10:58 PM
How's all our Non-US folks doing?
by djk - 07/23/21 09:13 PM
Do You Travel?
by Bill Addiss - 07/20/21 04:26 PM
Backup Generator Done Right
by timmp - 07/18/21 12:20 PM
New in the Gallery:
February, North East Indiana
February, North East Indiana
by timmp, July 25
Red Green would be proud
Red Green would be proud
by timmp, July 25
Who's Online Now
0 members (), 9 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#91517 01/20/05 07:32 PM
Joined: Jan 2003
Posts: 59
C
ccdave Offline OP
Member
a new cell site requiring its own metered service, fed off an 480/277 3ph 4wire BUT the new service panel is only providing 460 to a transformer on the roof, can that be done per code? It is a 3ph 4 wire service panel, neutral is for the meter and only 2 phases are being used--thanks

2017 / 2014 NEC & Related Books and Study Guides
#91518 01/25/05 11:59 PM
Joined: Mar 2001
Posts: 345
T
Member
Quote
ccdave a new cell site requiring its own metered service, fed off an 480/277 3phase 4wire BUT the new service panel is only providing 460 to a transformer on the roof, can that be done per code? It is a 3 phase 4 wire service panel, neutral is for the meter and only 2 phases are being used--thanks
"an 480/277 3 phase 4wire" WHAT? Is it a service, a switchboard, panel? Is the service panel in your posting the source of the feeder to the roof? When you say only two phases are being used may I conclude that you mean that the feeder will be single phase derived between two of the ungrounded conductors of the wye connected service panel? If the answer is yes than I see no problem. Single phase circuits, such as the circuit supplying the rooftop transformer, are run from three phase panels all the time.
--
Tom H


[This message has been edited by tdhorne (edited 01-25-2005).]


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Top Posters(30 Days)
timmp 8
Rachel 4
djk 2
Popular Topics(Views)
281,578 Are you busy
215,216 Re: Forum
202,053 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5