ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photo of the Week:

Delco-Light Generator
 Delco-Light Generator

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
1 members (Scott35), 27 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#91373 01/13/05 03:07 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
I'm adding a 125a subpanel on a residential job that has 2 200a main breakers at the meter feeding to 200a panels. Will feed the 125a with # 2-4cond copper from one of the 200a panels. Wondered how many sub panels I could feed off one 200a panel? Could I by code feed another, say 30 or 60a off the 125 amp? If the loads were low is there a limit on how many breakers can be used coming from the 200a panel?


The Golden Rule - "The man with the gold makes the rule"
Horizontal Ad
#91374 01/13/05 07:45 AM
Joined: Apr 2002
Posts: 7,401
Likes: 7
Member
Aldav:
I am not aware of any NEC restrictions on a quantity of sub-panels, as long as your load calcs are OK.

'Limits' are mechanically set by the mfg.
Basically....if you have a 42 circ 'main' the most you could connect to it are 20 sub's (fed by 2-pole cb's)

John


John

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 4,140
Joined: October 2000
Top Posters(30 Days)
BigB 6
Popular Topics(Views)
329,672 Are you busy
254,514 Re: Forum
237,009 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5