Bathroom Lights #91353
01/11/05 09:11 PM
01/11/05 09:11 PM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 610
massachusetts
I wired a bathrooms lighting circuit on a GFCI protected circuit.I also have a seperate 20 amp GFCI circuit for the plugs next to the sink.

Well the inspector doesn't want all the lighting on a GFCI circuit. He wants one light in the bath wired to another circuit seperate from the GFCI circuit that all the other lights are on.

Is there anything in the code requiring us to wire bathroom lighting like this? Maybe he is thinking of a old rule from a previous code...I can't find any rule in the 2002 NEC.

shortcircuit

2017 / 2014 NEC & Related Books and Study Guides
Re: Bathroom Lights #91354
01/11/05 09:53 PM
01/11/05 09:53 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,368
Estero,Fl,usa
No such requirement


Greg Fretwell
Re: Bathroom Lights #91355
01/12/05 12:18 AM
01/12/05 12:18 AM
P
Physis  Offline
Member
Joined: Dec 2004
Posts: 86
Burlingame, Ca. USA
I like to say that the inspector is welcome to run the idea pass the owner and or GC and if his proposal is accepted some one can give him an estimate for the cost of the changes he would like.


Sam, San Francisco Bay Area
Re: Bathroom Lights #91356
01/12/05 01:37 AM
01/12/05 01:37 AM
C
cpal  Offline
Member
Joined: May 2004
Posts: 162
Cohasset MA
There was a previous requirement in the Mass Code 1996 (210-70 d) that restricted all the lighting in an area from depending on a GFCI. The issue considered leaving the area in total darkness during the event of a failure of the GFCI. This requirement was deleted in 1999. The Committee recognized that nuisance tripping of these devices is less likely than previously encountered.

Re: Bathroom Lights #91357
01/12/05 01:40 AM
01/12/05 01:40 AM
K
kd  Offline
Member
Joined: Dec 2004
Posts: 52
Years ago, there was a requirement that every bedroom have outlets fed from two different circuits, but that is gone with the wind. Every violation should have a reference to the Code. Also the inspector is not the boss, the head of the building department is the boss.

Re: Bathroom Lights #91358
01/12/05 05:32 AM
01/12/05 05:32 AM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 610
massachusetts
cpal...thankyou for looking up the old code reference.I remember having to wire bath lights seperate from the load side of the bath GFCI plug so the lights wouldn't go out when the GFCI tripped.This was before 20 amp circuits were required for the bath plugs.

shortcircuit

Re: Bathroom Lights #91359
01/12/05 11:36 AM
01/12/05 11:36 AM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
From the 2005 Mass Electrical code " 210.70 (D) GFCI Protection of lighting outlets in all ocupancies. The operation of a single GFCI device shall not deenergize all lighting outlets in a given area." If the job is permitted after 1/01/05 Inspector is correct. If not you are ok. Why is the lighting circuit gfci protected anyway?

Re: Bathroom Lights #91360
01/12/05 01:34 PM
01/12/05 01:34 PM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 610
massachusetts
I have a exhaust fan/light over a shower that needs GFCI protection according to the instructions with the unit. I also have recessed lights over the cuzi tub which I like to have GFCI protected.

So I feed the 3-gang switch box for the lights in the bathroom with the load side of a GFCI plug located near the bathroom...in the master closet for the master bathroom.I'll locate a GFCI plug outside the bathroom in the upper hallway for the main bath.This way it is nearby for the homeowner to reset.

shortcircuit

Re: Bathroom Lights #91361
01/12/05 03:36 PM
01/12/05 03:36 PM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
I usually just use the receptacle gfci circuit to feed the fan if it is over a shower.

Re: Bathroom Lights #91362
01/12/05 08:35 PM
01/12/05 08:35 PM
N
Norstarr  Offline
Member
Joined: Sep 2004
Posts: 86
Wi
The code only requires the receptacle to be gfi protected. The code also states that if the separate 20 amp circuit to the bathroom is dedicated you can use it for the lighting and exhaust fans also for that one bathroom. Put the lighting on the line side of the gfi receptacle. Is his requirement for a second circuit for the lighting a local ordinance or his own preferance. If it isn't a local ordinance I would protest that he was missing when you quoted the job.
Ron

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 2
Khombo 2
Popular Topics(Views)
255,884 Are you busy
191,858 Re: Forum
181,623 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 15 (0.005s) Memory: 1.0236 MB (Peak: 1.1982 MB) Zlib enabled. Server Time: 2019-06-26 22:15:12 UTC