#91199 01/04/05 01:46 PM
Joined: Apr 2002
Posts: 178
R
Member
While visiting another furum I read a disscusion on sub panels.They must have 4 wires back to the main panel.They also stated in the main panel the neutral and grounds must be separated and not bonded together at main panel.If you have only 3 wire service at the main panel the grounds and neutrals would have to tie or the ground fault path wouldn`t trip the breaker. Did I totally miss something.was it a type o.

2017 / 2014 NEC & Related Books and Study Guides
#91200 01/04/05 02:01 PM
Joined: Nov 2003
Posts: 269
E
Member
I believe that either it was misstated in the discussion or you misread it but in the service equipment the EGC's and the service equipment enclosure are bonded to the grounded service conductor (i.e. the neutral). This provides the fault clearing path.


John
#91201 01/04/05 07:51 PM
Joined: Dec 2004
Posts: 86
P
Member
Do you mean:

[1] neutral
[2] (red) leg
[3] (black) leg
[4] Grounding conductor

The service does not provide a grounding conductor. That's why the service has only three conductors. The GEC at the service is where the grounding conductor comes from and it can only be connected to the service neutral at one point and that is at the service.


Sam, San Francisco Bay Area
#91202 01/04/05 07:53 PM
Joined: Dec 2004
Posts: 86
P
Member
After reading your post again. Did they leave out the main bonding jumper?


Sam, San Francisco Bay Area

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Top Posters(30 Days)
timmp 8
Rachel 4
djk 2
Popular Topics(Views)
281,578 Are you busy
215,216 Re: Forum
202,053 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5