4/0 service entrance conductors #91128 12/31/04 11:51 AM
Joined: Mar 2004
Posts: 16
J
JG Offline OP
Member
I recently saw a job with 4/0 al sevice single phase entrance conductors feed a 320 amp service, two 200 amp panels, a load calc of 228 amps. The engineer gave me a cut sheet listing the 4/0 at 315 amps, buried @90 deg C. Does this override 310.15 if 90 deg terminals are used?

2017 / 2014 NEC & Related Books and Study Guides
Re: 4/0 service entrance conductors #91129 12/31/04 03:12 PM
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
You are required to use table 310.16 for NEC installations unless you want to invoke
310.60D Engineering Supervision. I am not sure what you are considering terminations but if it the compression connectors that not
correct. The terminals are for the meter socket and any other connectors involved. Ratings per 316.16 for 4/0 AL is 180 amps.

Re: 4/0 service entrance conductors #91130 12/31/04 03:21 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline
Member
I have no idea how he came up with 315a. If I understand the question, you are talking about a Service lateral sized at 4/0. This is figured differently than an electrician would size Service Entrance conductors. The Utility company have a different rating system based on established demands.


George Little
Re: 4/0 service entrance conductors #91131 12/31/04 07:41 PM
Joined: Mar 2004
Posts: 16
J
JG Offline OP
Member
You are correct GL, it is a lateral, only customer owned. I was under the impression 310.15 must be adhered to, when not installed by the utility. Please correct if misguided.
Thanks

Re: 4/0 service entrance conductors #91132 12/31/04 08:28 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
JG are you asking about Table 310.15?

You may use that table in some applications you never have to use that table.

If this service lateral is customer owned and covered by the NEC the choices are Table 310.16 which would allow 180 amps per 4/0 AL or as option you could use Table 310.15 which would allow the 4/0 AL to run a 200 amp service.

Any chance you have two sets of 4/0 AL?

Any chance the 4/0 was copper not aluminum?

It is worth noting that the service conductors feeding two or more disconnects do not have to be rated as high as the total overcurrent protection.

Service conductors feeding two or more disconnects only have to be rated to handle the load.

With a load calc of 228 amps 4/0 AL is out of the question.

4/0 copper would do it with a rating 230 with a calculated load of 228. [Linked Image]

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: 4/0 service entrance conductors #91133 12/31/04 08:59 PM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member
We have a couple of local utilities that have us supply and install the service lateral conductors. The are sized and specd by the PoCo's engineering.

Re: 4/0 service entrance conductors #91134 12/31/04 11:27 PM
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
"We have a couple of local utilities that have us supply and install the service lateral conductors. The are sized and specd by the PoCo's engineering."
electure
When you do this does it become the property of the utiltiy?

Re: 4/0 service entrance conductors #91135 01/01/05 07:56 PM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member
Yes, it does. Is it different elsewhere?

Re: 4/0 service entrance conductors #91136 01/01/05 09:32 PM
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
electure
You are acting as a contractor for the utility. Since the NEC does not cover installations that are part of the distribution, they do not follow the same rules that the NEC applies to other installations. They caculate the load differently than required by section 220.
They estimate the load that will occur any give n moment and size the conductor to match this estimated load. That is why they can use 4/0 AL. In this case the conductor belongs to the home owner and it should be installed according the the NEC. In my opinion 4/0 is not large enough for this load.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,691 Are you busy
204,933 Re: Forum
193,045 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3