Kitchen counter top receptacles #91067 12/27/04 07:24 PM
Joined: Feb 2004
Posts: 133
E
Electric Ian Offline OP
Member
My understanding of 210.52(B)(3) is that the 20 Amp branch circuits that supply the kitchen contertop receptacles are permitted to supply additional receptacle outlets in the same kitchen, pantry or dining room. What about lighting outlets in the same kitchen. Is it permissible to tap a couple of recessed lights serving the kichen countertop from the 20 Amp branch circuit that supplies the countertop receptacles. I think the answer is no but I want to be sure. 210.52 still confuses me every time I reread it.

2017 / 2014 NEC & Related Books and Study Guides
Re: Kitchen counter top receptacles #91068 12/27/04 08:31 PM
Joined: Apr 2002
Posts: 7,211
HotLine1 Offline
Member
Ian:
To sum it up; NO

John


John
Re: Kitchen counter top receptacles #91069 12/27/04 09:20 PM
Joined: Feb 2004
Posts: 133
E
Electric Ian Offline OP
Member
Right. Didn't think so - Just wanted confirmation.
Thanks.

Re: Kitchen counter top receptacles #91070 12/27/04 09:30 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Here's the commentary from 210.52 B 1-3. It runs a little contrary to Hotlines remarks, but I would avoid adding lighting, or for that matter much else to kit circuits. "These circuits may also supply receptacle outlets in the pantry, dining room, and breakfast room, as well as an electric clock receptacle and electric loads associated with gas-fired appliances, but these circuits are to have no other outlets." meaning lighting etc. Although it requires 2 circuits I often will run 3 or more, depending on customer need or commonsense. And definately leave it seperate from lighting or other appliances like GB/DW.
http://www.markhellerelectric.com/21052B.pdf




[This message has been edited by e57 (edited 12-27-2004).]


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Kitchen counter top receptacles #91071 12/27/04 09:54 PM
Joined: Feb 2004
Posts: 133
E
Electric Ian Offline OP
Member
Got it. Thanks e57 for taking the time to make it crystal clear [Linked Image]


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,051 Are you busy
205,040 Re: Forum
193,164 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3