Hi,
I am wondering what to do about a ASER cable that the sheath some how got cut in several places along the middle section of a 50 foot run. It looks like a nail or some sharp edge that was hidden got a hold to it.

I cant reallt tell if the XHHW conductors were just scored or if the insulation was actually cut or not.

I hate to replace the cable if there is an acceptable way to use it.

Thanks for any replies or suggestions.

-regards

Greg

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#90871 12/16/04 09:06 AM
Joined: Jan 2004
Posts: 1,507
G
Member
Greg- Since the outer jacket would not figure in as the electrical insulation on the coductors, I'd remove the outter jacket where it was damaged and inspect the conductor insulation. If the conductor insulation and the uninsulated conductor are are not damaged, I'd use a good grade of plastic tape and tape the cable up and move on.


George Little
#90872 12/16/04 09:31 AM
Joined: Jul 2003
Posts: 26
S
Member
If there is any question at all, replace it. Ask urself is it worth the risk of the posible consiquenses of better to be safe.

#90873 12/16/04 09:32 AM
Joined: Feb 2004
Posts: 494
M
Member
George,
I was thinking that I could do that. The sections that have some cuts are accessible and I was thinking of using a few wraps some 33 on it. The sheath for this cable is very thin and not very durable.

As a matter of fact that is my opinion of all residential wire except UF. It seems to me they would make a tad bit tougher.

Thank you for the comment.

-regards

Greg

#90874 12/16/04 09:36 AM
Joined: Feb 2004
Posts: 494
M
Member
Sgreany,
Thanks for the input. I dont see where the conductors themselves were damaged. I think the code allows us to build the insulation back up to the original level and as long as there is no METAL lost on the conductor itself there current carrying capacity of the cable is as good as anything on the shelf.

I will put some 77 on first.

Safety is always my main concern.

-regards

greg


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Top Posters(30 Days)
BigB 6
Popular Topics(Views)
295,166 Are you busy
226,748 Re: Forum
211,906 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5