Receptacle ratings 15-20 #9085 04/16/02 08:26 PM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline OP
Member
May have been covered before but... An inspector told me today that a 15 amp duplex receptacle is not allowed on a 20 amp dedicated circuit. From what I read in the book this would be allowed 210.21(b)(1), (3)because this is not a "single receptacle" as defined by the NEC. He didn't push the issue and signed off on the job but for future reference I would like to hear other opinions.

Work Gear for Electricians and the Trades
Re: Receptacle ratings 15-20 #9086 04/16/02 08:49 PM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
You're right.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,004 Are you busy
205,006 Re: Forum
193,124 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3