#90567 11/30/04 11:25 AM
Joined: Apr 2002
Posts: 178
R
Member
What do you think of being told you can`t place a recessed can in a ceiling with no attic area. He maintains I can only install a old work can there.Not one with rails installed. He maintains no accses to juction box. Never heard this one.But I see a point almost but it can be taken out but not easily.Heck we do it all the time down stairs cans.Is there any justification for this.

Horizontal Ad
Joined: Feb 2002
Posts: 375
G
Member
The rails are just a convience for installing.

You can remove the assembly thru the light hole to gain access to the junction box.

Joined: Jan 2002
Posts: 1,457
E
Member
Another day another dope. Is this "He" claiming to be an inspector.

Joined: May 2004
Posts: 162
C
Member
410.67 Wiring.
(A) General. Conductors that have insulation suitable for the temperature encountered shall be used.
(B) Circuit Conductors. Branch-circuit conductors that have an insulation suitable for the temperature encountered shall be permitted to terminate in the luminaire (fixture).
(C) Tap Conductors. Tap conductors of a type suitable for the temperature encountered shall be permitted to run from the luminaire (fixture) terminal connection to an outlet box placed at least 300 mm (1 ft) from the luminaire (fixture). Such tap conductors shall be in suitable raceway or Type AC or MC cable of at least 450 mm (18 in.) but not more than 1.8 m (6 ft) in length.

This has been in the Code in one form or another for quite a while. The placement of the outlet box one foot away was for maintenance.
The 6 feet (used to be 4-6 feet)of suitable raceway allowed you to drop the can out of the ceiling and get it out of your face to get in to the J box one foot away to service the branch circuit conductors. Another theory was the (4) to 6' that used to be required (before pre-wired fixtures I think 1996 or 99) allowed the fixture wires to cool before they contacted the old 60 degree Cel. wiring at the branch circuit J box . The old recessed cans used to come with a snap on J box no pre wire no fixture wire.


BTW unless otherwise listed your installation should be acceptable
Charlie

[This message has been edited by cpal (edited 11-30-2004).]

Joined: Dec 2004
Posts: 209
H
Member
Reel-Break,

I was tripped up on this one some years back. It was with a recessed fixture, rated for thru-branch wiring, but it had a small opening. There is a problem with the UL listing of the fixture. UL list recessed fixtures with an opening smaller than 6" to have its junction box very close to the opening to be rated for thru branch wiring. I forget the equation, but it has to do with adding the distance horizontally and vertically that the bos is located from the opening and comparing this amount to the diameter of the opening. If you need it, I'll look it up


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Top Posters(30 Days)
BigB 4
Popular Topics(Views)
327,703 Are you busy
252,561 Re: Forum
235,175 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5