ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 228 guests, and 10 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Oct 2004
Posts: 265
D
dmattox Offline OP
Member
Section 422.31 (B) "... circuit breaker is within sight from the appliance or is capable of being locked in the open position."

Would being able to lock the panel door meet this requirement?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Nov 2003
Posts: 269
E
Member
Interesting question. IMO it would since you are accomplishing the same thing as locking the breaker.


John
Joined: Oct 2000
Posts: 2,749
Member
See the change in the 2005 NEC:

Quote
422.31 Disconnection of Permanently Connected Appliances.

(B) .......the branch-circuit switch or circuit breaker shall be permitted to serve as the disconnecting means where the switch or circuit breaker is within sight from the appliance or is capable of being locked in the open position. The provision for locking or adding a lock to the disconnecting means shall be installed on or at the switch or circuit breaker used as the disconnecting means and shall remain in place with or without the lock installed.


Joe Tedesco, NEC Consultant
Joined: Oct 2004
Posts: 265
D
dmattox Offline OP
Member
Joe,

Isn't that just talking about one of those plastic locking devices that cover a breaker, saying thats not enough.

"..installed on or AT the switch or circuit breaker..."

That shows that it does not actually have to be installed on the breaker to me.