Joined: Feb 2004
Posts: 494
M
Member
Hi,
is it required to disconnect all communications when an E-stop is activated in a Classified area...like at a fueling station?

Art. 514.11 is disconnects and 514.13 is all about maint.

thanks for any replies..

-regards

Mustang

[This message has been edited by mustangelectric (edited 11-02-2004).]

[This message has been edited by mustangelectric (edited 11-02-2004).]

2017 / 2014 NEC & Related Books and Study Guides
Joined: Jan 2004
Posts: 1,507
G
Member
Mustang, I'm not sure what you are calling a "fueling station" but if it is a gas station look at 514.11 and 514.13. Your post made me get the book out but that's okay. [Linked Image]


George Little
Joined: Feb 2004
Posts: 494
M
Member
Hi,
thanks for the reply. Yes this is a gas station. the inspector wants all communications and computers to comply with art 514.11 and 514.13 which I say we do becasue the pumps are shunt trip and as I understand it this does not disconnect the communications or computers...514.13 covers MAINTENANCE and to do that all you need to do is operate the OCPD or disconnect the attachment plug for the device..

follow me?

thanks for any replies..

-regards

Mustang

[This message has been edited by mustangelectric (edited 11-02-2004).]

Joined: Jul 2002
Posts: 680
W
Member
Where are these communications?? In a classified area??.Are they in a kiosk? How does a shunt trip switch the neutral??

Joined: Feb 2004
Posts: 494
M
Member
Hi,
The communications is a call button and speaker mounted at the dispenser..

This is a classified area up to 18". Shunt trip opens grounded and ungrounded conductors..

-regards

Mustang

Joined: Jul 2002
Posts: 680
W
Member
You have a 3 pole shunt trip? that has a space for the neutral(grounded conductor)? If so who makes it?, thats alot easier than a relay.
Interesting point on call button and speaker, don't use call buttons and speakers are generally built into pump but could cause a spark. Never seen the speakers shut off with a panic button.

Is this location unattended?

Joined: Feb 2004
Posts: 494
M
Member
Hi,
This is an attended public fueling station. There is a relay and there is a shunt trip I cannot say who makes it but I can try and find out. I am thinking Cutler Hammer.

The article 514.11 is talking about disconnecting the circuit to the dispenser pump and any auxillary power such as for lighting. It does not address the low voltage circuits. Article 514.13 is talking about maintenance and being able to remove power to communications and computers etc. but for maint. not emergency. If I am interpreting it coreectly..

thanks for the replies..

-regards

Mustang

Joined: Jul 2002
Posts: 680
W
Member
If its an attended self serv, I don't see where the NEC requires an E Stop that shuts all dispensers down at once.

Joined: Feb 2004
Posts: 494
M
Member
Hi,
Please see 514.11 (a)for requirement.

-regards

Mustang


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Top Posters(30 Days)
Admin 14
Trumpy 10
Popular Topics(Views)
280,364 Are you busy
213,440 Re: Forum
200,360 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5