Range hoods require an individual branch circuit #89916 10/24/04 03:18 PM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
Look at what is NEW in Article 422 for cord and plug connected Range Hoods!

.......

Quote
(5) The receptacle shall be supplied by an individual branch circuit.


[See ROP 17–21]

Why? What was the substantiation?


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Range hoods require an individual branch circuit #89917 10/24/04 03:26 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
That is a good question Joe.

Do you mind if I just guess at the substantiation?

Could it be that it is expected a microwave hood combo unit may be installed at some later date?

I hope I am wrong about that.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Range hoods require an individual branch circuit #89918 10/24/04 03:39 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Not making light of the issue, but I must live a sheltered life in that I have never installed a cord and plug connected range hood.

Roger

Re: Range hoods require an individual branch circuit #89919 10/24/04 03:52 PM
Joined: Jun 2004
Posts: 206
C
capt al Offline
Member
Roger, guess I have lived the same way. Never installed one in the 25 years I've been doing electrical work. Every range hood I have connected was hard wired.

Al

Re: Range hoods require an individual branch circuit #89920 10/24/04 04:00 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Hello Al, whew, I'm glad I'm not alone here. [Linked Image]

Roger

Re: Range hoods require an individual branch circuit #89921 10/24/04 04:04 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
Roger and Al where did you locate the disconnect switch?

Not in the cabinet I hope, that would be a 110.26 violation. [Linked Image]

Just kidding I have only seen hard wired hoods also.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Range hoods require an individual branch circuit #89922 10/24/04 06:28 PM
Joined: Jun 2003
Posts: 681
P
PCBelarge Offline
Member
One reason you guys may not have seen a cord connected range hood is that they are sold at the Big Box stores and usually not installed by 'electricians'.

422.16(B)(4)Range Hoods.
Range hoods shall be permitted to be cord-and-plug connected with a flexible cord identified as suitable for the use on range hoods in the installation instructions of the appliance manufacturer, where all of the following conditions are met:


Bob, your reasoning is right on the money! See page 206 of the 2005 Analysis book.


Substantiation:
Many times range hoods are removed and replaced with a "microwave type" range hood. Allowing cord and plug connection will make the installation much easier for the homeowner because no "electrical change" to the wiring system will be required.

Panel Statement:
The permission to use cord-and-plug connection provides the ability to upgrade to a combined microwave range hood. The panel added the additional requirements to ensure a safe installation of a combined microwave range hood.


***This statement and code change says something to me that makes me very uneasy. Why is the NEC making code changes based on Homeowners performing installations. ELECTRICIANS should be installing electrical work and using the NEC as well as their learned skills from the field.****

Pierre


Pierre Belarge
Re: Range hoods require an individual branch circuit #89923 10/24/04 06:37 PM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
I agree Pierre. It sure seems strange that this passed. How many proposals do you see that really are good ideas but have no technical substantiation and get shot down because of it? It seems to me that this is no diffferent than the rest of them.


Ryan Jackson,
Salt Lake City
Re: Range hoods require an individual branch circuit #89924 10/24/04 06:51 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
Pierre

Quote
This statement and code change says something to me that makes me very uneasy. Why is the NEC making code changes based on Homeowners performing installations. ELECTRICIANS should be installing electrical work and using the NEC as well as their learned skills from the field


Well said.

I also think of this.

Quote
This Code contains provisions that are considered necessary for safety. Compliance therewith and proper maintenance will result in an installation that is essentially free from hazard but not necessarily efficient, convenient, or adequate for good service or future expansion of electrical use.


With this reasoning 30 and 50 amp outlets should be provided at gas dryers and ranges in case the homeowner decides to change to electric in the future.

We better run 10/3 to this hood outlet in case the microwave hood combo that might be installed has browning elements.

Well I can't complain as I was not involved in the code making process. [Linked Image]

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Range hoods require an individual branch circuit #89925 10/24/04 07:54 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
I have been giving residential hoods thier own circuit for years. Most of the higher end ones really suck if you know what I mean, multiple motors, lighting, heat lamps, etc. Some will pull upwards of 12A. Justification alone for a dedicated circuit. However, I haven't seen one cord connected yet either??? Where would one place a plug for such an animale?


Mark Heller
"Well - I oughta....." -Jackie Gleason
Page 1 of 3 1 2 3

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
sparky 10
Popular Topics(Views)
259,660 Are you busy
195,033 Re: Forum
184,447 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3