Photos of the Week:
Avalon Theatre
Avalon Theatre-1 2 3 4
Random Gallery Image:
0 members (), 97 guests, and 47 robots.
#89903 10/23/04 09:20 PM
dmattox Offline OP
On a job I am doing, the building inspector(not the electrical inspector) is requiring us to bond to the cold water even though it is PVC in the ground. The only requirement that I know of for a cold water is to bond it as a grounding electrode, but since its PVC that doesn't apply. Is there any section of the NEC that just requires cold water to be bonded?
Worst part is that this is actually 4 suites, and he wants all the suites bonded. We are bonded to building steel and the ufer, which satifies grounding electrode requirements of the NEC.
#89904 10/23/04 09:31 PM
Ron Offline
250.53 requires bonding when the water pipe is used as a grounding electrode.
250.104 requires bonding of the water pipe in the event it becomes energized within the residence.
Ron
#89905 10/23/04 11:07 PM
dmattox Offline OP
ah, never noticed 250.104. Thanks Ron.