#89759 10/18/04 01:19 PM
Joined: Oct 2004
Posts: 6
N
nojkj Offline OP
Junior Member
Hi I got this question on test

Tap existing service to new location
1 special permission
2 used approved material for connection I put only no 2 but what do you think.
a) only no 1
b) only no 2
c) both 1 and 2
d) neither 1 or 2 ( I put b but my feeling it is c but I do not find anything in the code that support than
Thanks Jon

Horizontal Ad
#89760 10/19/04 03:32 PM
Joined: Mar 2003
Posts: 849
Y
Member
230.46 is all I can think Of? 2002 N.E.C.

#89761 10/19/04 04:47 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
No. See 230.40 exception 2.
This is kind of a trick question though. A service conductor can never really be "tapped", since there is no way to meet the definition of a tap with a service conductor in 240.2. The only true "taps" allowed in the NEC are for feeders and (under rare circumstance) branch circuits.

If you are asking if you can install a second set of service entrance conductors on one service, the answer is yes, using the above cited reference. Be careful to satisfy the requirement of conductor per terminal in 110.14, as I have not seen a meter enclosure that has provisions for two condutors per leg and per nuetral.

I would answer "D" and then I would jot down the question number to use as a challenge in case you get it wrong, citing 240.2, definition.

[This message has been edited by Ryan_J (edited 10-19-2004).]


Ryan Jackson,
Salt Lake City
#89762 10/19/04 06:37 PM
Joined: Mar 2003
Posts: 849
Y
Member
Definitions. Service conductors(Service Point to service Disconnecting means)
Say you Run 500s to a Wireway Then (TAP) 4 100 amp SERVICE disconnecting means off The 500s (allowed up to six same location(230.71)
By code that IS allowed and commomly used .

#89763 10/19/04 07:10 PM
Joined: Mar 2003
Posts: 849
Y
Member
Point of Info See N.E.C. 2002 Analysis of Changes put out by I.A.E.I. Page 90 in reference to 230.46 Shows an Example of what I said in the pervious post.

#89764 10/19/04 08:20 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
I do it a lot, and require no special permission, and yep more than six would require a fused main disco. In some areas special permission may be required. So I say #2 is a viable answer.

Quote
230.46 Spliced Conductors.
Service-entrance conductors shall be permitted to be spliced or tapped in accordance with 110.14, 300.5(E), 300.13, and 300.15.
Splices are permitted in service-entrance conductors if the splice meets the requirements of 230.46. Splices must be in an enclosure or be direct buried using a listed underground splice kit. It is common to have an underground service lateral terminate at a terminal box either inside or outside the building. At this point, service conductors may be spliced or run directly to the service equipment.
Splices are permitted where, for example, the cable enters a terminal box and a different wiring method, such as conduit, continues to the service equipment. Splices are most common where metering equipment is located on the line side of service equipment, service busways, and taps for supplying up to six disconnecting means.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#89765 10/19/04 08:23 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
I usually do it in a gutter, or can, prior to multiple meter/main panels. Our utility only requires provision for a wire seal.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Horizontal Ad
#89766 10/19/04 09:09 PM
Joined: Oct 2004
Posts: 6
N
nojkj Offline OP
Junior Member
Thanks Its litle confusing but the answer are either b or d but its hard to tell because there is nowhere talked about existing service in the code but 230 33 and 230 46 talk about tapped and after reading 240 2 b.

#89767 10/20/04 08:19 AM
Joined: Aug 2003
Posts: 1,374
R
Moderator
It is impossible to meet the definition of tap with a service conductor since it is specifically addressed in the definition of tap.

If the question is can I splice, the answer is yes. If the question is can I tap, the answer is no.


Ryan Jackson,
Salt Lake City
#89768 10/20/04 08:47 AM
Joined: Oct 2004
Posts: 6
N
nojkj Offline OP
Junior Member
Hi and thanks for your response you would say No to tap even after reading 230 33 230 46 where is talk about both spliced or tapped??
Thanks Jon

Page 1 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,443
Joined: July 2002
Top Posters(30 Days)
Popular Topics(Views)
340,084 Are you busy
265,525 Re: Forum
246,539 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5