Intrinsically Safe Circuit #89690
10/13/04 08:59 AM
10/13/04 08:59 AM
M
mustangelectric  Offline OP
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
hi,
if i seal a conduit as required in a classified area, does this satisfy the requirement for rating a circuit as intrinsically safe?

thanks for any replies.

mustang


Electricity has no respect for ignorance!
2017 / 2014 NEC & Related Books and Study Guides
Re: Intrinsically Safe Circuit #89691
10/13/04 02:12 PM
10/13/04 02:12 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,368
Estero,Fl,usa
The short answer is no.
Intrinsically safe circuits are those that do not have the energy to cause a spark, it has nothing to do with protection.

See 504 definitions


Greg Fretwell
Re: Intrinsically Safe Circuit #89692
10/13/04 04:07 PM
10/13/04 04:07 PM
M
mustangelectric  Offline OP
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
so if i run lighting to a pump house in an oilfield that is classified class 1 div 1 or class 1 div 2, then those ckts have to be intrinsically safe?

i never saw an intrinsically safe thhn..i have seen shielded cables and explosion proof fittings and enclosures...

the question came up because an inspector is requiring INTRINISCALLY SAFE CKTS at a refuleing station!

some of the control and POS is intrinsically safe but the rest of the building and ckts are normal ckts...these are in unclassified locations...

what could he mean?

here is the exact quote:

"COMPLY NEC 514.11 AND 514.13/SPECIFY ALL CIRCUITS INCL INTERCOMS, LO VOLT CONTROLS, COMPUTERS, INTRINSICALLY SAFE, ETC)."

these articles have nothing to do with intrinsic ckts...that i could tell..

thanks for the replies

mustang

[This message has been edited by mustangelectric (edited 10-13-2004).]

[This message has been edited by mustangelectric (edited 10-13-2004).]


Electricity has no respect for ignorance!
Re: Intrinsically Safe Circuit #89693
10/13/04 05:35 PM
10/13/04 05:35 PM
T
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
did the inspector just want disconnects that comply with those sections? I interpret the end of that quote as some kind of labeling/indentification requirement.

[This message has been edited by trekkie76 (edited 10-13-2004).]

Re: Intrinsically Safe Circuit #89694
10/14/04 05:01 PM
10/14/04 05:01 PM
M
mustangelectric  Offline OP
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
hi,
i am working from code comments...never spoke to him...maybe it will take a phone call or e-mail to figure it out..

i am still trying to figure it out!

thanks for the replies..

mustang


Electricity has no respect for ignorance!
Re: Intrinsically Safe Circuit #89695
10/14/04 07:09 PM
10/14/04 07:09 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Quote
so if i run lighting to a pump house in an oilfield that is classified class 1 div 1 or class 1 div 2, then those ckts have to be intrinsically safe?

I don't think that it is even possible to have an intrinsically safe lighting circuit. For an instrinsically safe circuit there must be no possible way to cause a spark that has enough energy to ignite the gasses, even if you short the conductors. Lighting would have to be of the type approved for the area classification and the raceways and seals will have to comply with Article 501.
Don


Don(resqcapt19)
Re: Intrinsically Safe Circuit #89696
10/14/04 07:11 PM
10/14/04 07:11 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Quote
"COMPLY NEC 514.11 AND 514.13/SPECIFY ALL CIRCUITS INCL INTERCOMS, LO VOLT CONTROLS, COMPUTERS, INTRINSICALLY SAFE, ETC)."

Is this installation a gas station? That is the application of Article 514. It does not apply to other classified areas.
The code sections cited require that there be a means of disconnect for all circuits of any type that serve a fuel dispensing unit, and do not apply to any other classified areas.
Don



[This message has been edited by resqcapt19 (edited 10-14-2004).]


Don(resqcapt19)
Re: Intrinsically Safe Circuit #89697
10/14/04 09:25 PM
10/14/04 09:25 PM
N
Norstarr  Offline
Member
Joined: Sep 2004
Posts: 86
Wi
Mustang,
I have found that you have to really educate yourself regarding hazardous locations. A lot of inspectors are not completely informed of the requirements and therefore make guesses. If you are installing a light fixture it can not be made intrinsically safe. It must be a fixture rated and listed for the hazardous location with the proper raceway and seals. Usually only control items can be made intrinsically safe, such as float switches etc, using the proper components.
I had an inspector walk in on a job I did and condemned the job as soon as he saw thinwall. Kept repeating "All wiring in a hazardous location must be in rigid". He could not understand "intrinsically safe". Took a lot of my time meeting with him and his boss to get it approved. Because I took the time to read and read until I understood hazardous location wiring I was able to stand there, proud of the job, knowing I would not have to change anything. I'm sure if you ask the inspector face to face what his interpretation is you will both learn and the job will be safe.
Ron


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Khombo 2
Popular Topics(Views)
255,882 Are you busy
191,857 Re: Forum
181,620 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.034s Queries: 14 (0.005s) Memory: 0.9957 MB (Peak: 1.1561 MB) Zlib enabled. Server Time: 2019-06-26 16:48:34 UTC