control transformer #8967
04/10/02 02:09 PM
04/10/02 02:09 PM
J
Joe Carpenter  Offline OP
Member
Joined: Dec 2001
Posts: 50
USA
What is the downside to using a 240v primary/ 24 secondary transformer for a 120v primary/ 12v secondary application? I know it works but is there a reason I should not do it if I size it for the correct kva? I need to use it to power 12volt automotive lights.
Thanks

Work Gear for Electricians and the Trades
Re: control transformer #8968
04/10/02 08:10 PM
04/10/02 08:10 PM
D
donles  Offline
Member
Joined: Apr 2001
Posts: 83
Pennsylvania
Hi Joe,
I don't think there is a down side as long as it's rated properly. The rest is turns-ratio - i.e. they are the same.
Don

Re: control transformer #8969
04/10/02 11:35 PM
04/10/02 11:35 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Remember that you need to halve the transformer VA, too. Current remains constant.

Re: control transformer #8970
04/11/02 11:27 PM
04/11/02 11:27 PM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
Are you planning to use a Transformer with single windings on both sides [Primary and Secondary]? And this Transformer is rated only as 240 Pri / 24 Sec.?

If the Volt-Amp rating [VA or KVA] was 250 VA for this Transformer, and you plan to drive it at 120 VAC, only load it up to 125 VA. Otherwise it will burn out.

125 VA @ 12 VAC would be around 10.3 amps.

Falling under the 125 VA rating assures the smoke remains inside the windings [Linked Image]

If the transformer has "Split Windings", then connect the windings as needed to be driven from 120 VAC and output of 12 VAC.

If only one side has split coils, leave the arrangements as 240 VAC Pri / 24 VAC sec.

I used a very large rating for a Control Transformer [250 VA]. They are usually around 25 VA min. to 100 VA max., with 50 VA being a normal rating.

If you plan to drive an Automotive Headlamp, you should consider a larger Transformer.

Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 4
Popular Topics(Views)
249,447 Are you busy
187,361 Re: Forum
176,700 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.9599 MB (Peak: 1.0912 MB) Zlib enabled. Server Time: 2018-09-25 03:13:52 UTC