New Ground Rod #89518
09/23/04 12:08 PM
09/23/04 12:08 PM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,498
Michigan USA
Have any of the group viewing this BB had any exposure to the new "5/8" inch galvanized ground rod manufactured by Galvan? The rod is listed but it is not "5/8" inch. Are the inspectors approving same based on the wording at NEC 250.52(A)(5)? Check it out at: http://www.galvanelectrical.com


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: New Ground Rod #89519
09/23/04 11:07 PM
09/23/04 11:07 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Not sure what the advantage over CU-clad would be....Cost?

But this seems to be within the wording of the code.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: New Ground Rod #89520
09/24/04 12:19 AM
09/24/04 12:19 AM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,498
Michigan USA
We have some inspectors that maintain that a galvanized rod must be 5/8" diameter. The Galvan rod is just a touch over 1/2" in diameter. Based on my research, with UL and NEMA, the Galvan rod does not have to be 5/8" and coplies with 250.52(A)(5)(b). even though it is a steel rod that has been galvanized.


George Little
Re: New Ground Rod #89521
09/30/04 03:52 PM
09/30/04 03:52 PM
M
mustangelectric  Offline
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
hi,
i was wondering about this a year or two ago. i do not use galvanized rods myself. i know they are cheaper but there is always a chance for some question about the acceptability of this type rod that i just stick with copper.

all the ones i have ever seen are the small 1/2" ones..i never use any type of 1/2" rods, 5/8 is the min for me..1/2" will bend too easy!

-regards

mustang


Electricity has no respect for ignorance!

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Khombo 2
Popular Topics(Views)
255,882 Are you busy
191,857 Re: Forum
181,620 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.038s Queries: 14 (0.005s) Memory: 0.9596 MB (Peak: 1.0923 MB) Zlib enabled. Server Time: 2019-06-26 16:34:37 UTC