ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Prototype production service needed
by carmend12345. 09/24/18 04:40 AM
220/230/240V 60Hz Systems
by gfretwell. 09/23/18 02:50 PM
Inspection camera help
by petey_c. 09/22/18 07:52 AM
Motion detectors and dimmers
by gfretwell. 09/20/18 04:02 PM
Extension cords
by annemarie1. 09/20/18 08:54 AM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
0 registered members (), 8 guests, and 22 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
two power sources in same enclosure #89076
08/30/04 12:46 PM
08/30/04 12:46 PM
J
joebarilovits  Offline OP
Junior Member
Joined: Aug 2004
Posts: 1
Simpsonville, SC, Greenville
I'm building a heater temperature control system in one enclosure for a customer. The customer requested that they will supply the enclosure with a 120VAC single phase 10A control power and 480VAC 3-phase 30A power for the heater. Does the NEC require any warning signs be posted on the outside of the enclosure to notify the user that the system is supplied by two power sources?

2017 / 2014 NEC & Related Books and Study Guides
Re: two power sources in same enclosure #89077
08/30/04 06:33 PM
08/30/04 06:33 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
That is one reason why MCC cubicles {buckets} and combination starters are available with 480:120V control-power transformers — to limit hazardous/foreign voltages [below the disconnect line terminals] when the disconnect is opened.

Re: two power sources in same enclosure #89078
08/30/04 08:24 PM
08/30/04 08:24 PM
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Research Article 424, and see this because the logic is considered:

Quote
430.113 Energy from More Than One Source.

Motor and motor-operated equipment receiving electrical energy from more than one source shall be provided with disconnecting means from each source of electrical energy immediately adjacent to the equipment served.

Each source shall be permitted to have a separate disconnecting means. Where multiple disconnecting means are provided, a permanent warning sign shall be provided on or adjacent to each disconnecting means.

Exception No. 1: Where a motor receives electrical energy from more than one source, the disconnecting means for the main power supply to the motor shall not be required to be immediately adjacent to the motor, provided the controller disconnecting means is capable of being locked in the open position.

Exception No. 2: A separate disconnecting means shall not be required for a Class 2 remote-control circuit conforming with Article 725, rated not more than 30 volts, and that is isolated and ungrounded.


Joe Tedesco, NEC Consultant
Re: two power sources in same enclosure #89079
09/02/04 06:23 AM
09/02/04 06:23 AM
B
Big Jim  Offline
Member
Joined: Jul 2003
Posts: 394
Denver, CO USA
In my industrial facility, we were required by OSHA to post signs on our panels indicating Dual Voltages and Multiple Voltages where that applied.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 9
Popular Topics(Views)
249,428 Are you busy
187,352 Re: Forum
176,691 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.003s) Memory: 0.9603 MB (Peak: 1.0933 MB) Zlib enabled. Server Time: 2018-09-24 13:28:32 UTC