#88894 08/11/04 05:08 PM
Joined: Aug 2004
Posts: 1
T
TCIG Offline OP
Junior Member
I am installing pneumatic lift tables for raw materials on a plant floor. I need to get 120VAC (20 Amp circuit) to the lift table to power the pump motor and the up/down controls. It has been requested that these tables be removable.

We are not willing to pay for installing conduits underground. As the tables must be removable, it has been requested that any conduit coming down from up above be flexible with a plug-in connector so we can unplug the table and tie the flexible conduit up overhead in order to clear room for forktrucks that occasionally need to go through this area during projects.

I am basically considering running RMC overhead (12-15 feet up) until it 90's downward, at which point it will become flexible metallic conduit (sealtight) or flexible nonmetallic conduit (corr-lock) with a plug near the ground. Are there any code violations described in this plan?

Thanks,

TCIG

2017 / 2014 NEC & Related Books and Study Guides
#88895 08/11/04 06:41 PM
Joined: May 2004
Posts: 162
C
Member
I would suggest you look at 400.7 (A)(6)

400.7 Uses Permitted.
(A) Uses. Flexible cords and cables shall be used only for the following:
(6) Connection of utilization equipment to facilitate frequent interchange

It may be acceptable to your installation

Charlie

#88896 08/13/04 11:41 PM
Joined: Jul 2004
Posts: 29
K
Member
I've seen some similar installations for a commercial bakery and a small manufacturing plant. The Inspector insisted on boxes at the joist line, with a blank cover, and Kellems-grip cord connector out the side with 12/3 SO cord down to the twistlock cord connectors. They hung at about 7' above the floor so most people and fork lifts could get by without hitting them. Would be worth looking into, and checking with the local AHJ to be sure before installing.


Even a blind hog can find an acorn every now and then

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Top Posters(30 Days)
Trumpy 10
Admin 10
Popular Topics(Views)
280,438 Are you busy
213,522 Re: Forum
200,401 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5